DC GFCI [RE-wrenches]
Christopher Freitas - OutBack Power
cfreitas at outbackpower.com
Fri Jan 11 15:48:20 PST 2002
Drake Chamberlin - Electrical Energy wrote:
> The ground fault detector is near the batteries not the array. In the
> event of a nail through a cable, shorting positive to ground, wouldn't
> the circuit from the array continue to short even if the device were
> tripped?
If the "nail through the cable connected postive to negative - yes
current would still flow from the PV array and no hazard would be
present (except for the nail itself). There would not be a "ground
fault" in essence. The breaker on the battery may or may not trip (C40
controllers have very fast electronic protection - faster than breakers)
or the impedance of the cabling may also limit fault currents. Or the
system might be batteryless.
If the nail connected the positive or negative conductor to the
grounding system then the DC-GFP would trip and the PV array would be
disconnected from the rest of the system. The DC bond from the negative
to ground would be switched from low impedance (less than an ohm) to
high impedance (50,000 ohms) to limit the current flowing in the fault
and the grounding system.
It is hard to imagine all of this in ones head - you need to draw it out
to really see. Kinda hard to do on a list...
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list