I never did understand what it's protecting.  I don't remember anything
about a Canadian lab questioning them.  That does sound an awful lot like
what I posted, though.

The main problem I saw, and still do see with them was as such;

A fault happens somewhere in between the inverter and the roof mounted
panels.  The GFP detects this fault and opens the circuit.   Since the
panels are still producing power the fault is still merrily smoldering away
on the roof or in the attic until sunset.  Hopefully the customer notices
the breaker is tripped before the house catches fire.

Wow, now that's helpful a device.

Travis Creswell
Ozark Energy Services, Inc.
----------
>From: Drake Chamberlin - Electrical Energy <solar at eagle-access.net>
>To: RE-wrenches at topica.com
>Subject: DC GFCI [RE-wrenches]
>Date: Fri, Jan 11, 2002, 1:08 PM
>

>Long ago, someone on the list mentioned that personnel in a Canadian Lab 
>felt that the DC GFCI, mounted near the batteries, for roof mounted systems 
>wasn't an effective safety device.
>
>Does anyone remember the reference on that?
>
>Thanks,
>
>Drake
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list