searching for news of Sunny Boy [RE-wrenches]
Doug Pratt
dpratt at pacific.net
Sat Sep 8 21:32:58 PDT 2001
-----Original Message-----
From: William Miller [mailto:wrmiller at slonet.org]
<snip>The configuration has this disadvantage: The only available unit
is 2500
watts. It requires 24 12 volt nominal modules in series. It has been
difficult for us to put together a scaleable package--one in which the
client can start with a smaller array and increase as funds allow.
<snip>
You can make the Sunny Boy 2500 slightly scaleable by using 75-watt
modules. Start with a single string, add a second string when money
allows. It'll comfortably accept two 75-watt strings of 21 to 23
modules.
Also, be careful about how many modules you put in a series string.
Depending on the particular module selected, and the climate, the
"correct" number can vary from about 18 to 24. John Berdner has a great
little spreadsheet program for the SB2500 that'll keep you outa trouble.
Have him email you a copy.
-Doug Pratt
- - - -