Ethical dilemma [RE-wrenches]
Bill Hoffer
Billhoffer at hotmail.com
Tue Aug 14 09:52:20 PDT 2001
William Miller wrote:
> Fiends:
>
> Here's a dilemma and how I dealt with it. I am still wondering if there
> is
> a better solution. Your thoughts are appreciated:
>
> I was called by the operations director for an off-grid elementary
> school
> to replace fans on an SW inverter. While on site, I took some time to
> learn how the system was built. There are 4 SW inverters with outputs
> summed through 2 levels of transformers. They run their generator
> during
> the school day and ran on batteries and inverters during the afternoon
> and
> evening for extra curricular, janitoring and etc. The system runs great
> while fed by the generator, but when the generator shuts down, inverters
> 1
> and 2 are not synced to inverters 3 and 4. You can measure the voltage
> from phase to phase and over a half hour or so it goes from 240 to 0 and
> then back up. The output of the equipment room is two hots and a shared
> neutral. When the inverters are out of phase, the neutral is properly
> shared. When the inverters drift in phase, the neutral current will
> increase, possibly until the current is double the rated current. It is
> my
> understanding that power is distributed throughout the school in this
> manner. At any point where a neutral is shared--on a feeder or
> multi-wire
> branch circuit--this condition is possible.
Sounds like a really bad install by someone who doesn't have a clue! I
am assuming that this is a series/parallel set up supplying 240. Trace
experimented (there are several functioning systems out there) with
series/paralleling 4 SW inverters. For awhile they actualy supplied a
connection to keep all 4 inverters in sync, 2 parallel and 2 in series.
I am guessing that this set up does not have the 4 inverters
interconnected properly. There are also some special programming tricks
that need to be done to the inverters to insure that the #1 inverter
always takes the lead and the other inverters follow when the inverters
connect to outside sources (Gen and Grid) and when they disconnect. And
also timed relays were needed to insure that the #1 inverter saw and
reacted to the inputs first. It really is not so bad once you
understand what is happening, but I would not recommend it unless you
are very experienced and have time to play with it (and a few spare
inverters in case you blow one!) Unfortunatly the only guy who knows
how to make it work, no longer works at Trace/Xantrex! > William
>
> __________________________________________________________________
> William Miller
> SLO Communications: Communications and Power Systems Consulting
> PO Box 50, Santa Margarita, CA 93453
> Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
> email: wrmiller at slonet.org
> License No. C-10-773985
> _____________________________________________________________
> Compatibility:
> Word processor: WP7
> Spreadsheet: Quatro Pro 7
> CAD: Microstation 95, DXF, Visio 4.1T
> _____________________________________________________________
> "I stand by all the misstatements that I've made." Dan Quayle
> __________________________________________________________________
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list