Hey Bob,
    I've got the Progen 5000 and had the same problem when using it with my
DR3624 inverter. I've had no luck at all with the so called full power
outlets on these gensets. Instead, I used the Trace T240 to balance the
genny output and also bumped the rpms up to around 3700. I now get 72 amps
out of the Progen/ DR3624 combo.....as opposed to 30-35 amps previously.
    And before anyone jumps on me about cruelty to generators....with 50
hour oil changes and basic preventive maintenance, I now have over 3000
hours on this baby. Running great....only had to replace the muffler so
far.

Roy Butler
Four Winds Renewable Energy
Arkport, NY

- - - -