Trace/Onan starting [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Thu Jul 12 13:25:15 PDT 2001


Drake is correct. Also, you need Rev 4 SW software. Rev.3 may work (I can't
remember anymore) but has other limitations. If the SW is not Rev.4, it may
be simpler to purchase the TWS (Two Wire Start) option from Onan, which
makes the start algorithm work like a Kohler.
Allan

----- Original Message -----
From: Drake Chamberlin - Electrical Energy <solar at eagle-access.net>
> Hi Dave,
>
> The Onan requires that the GLOWSTOP function in menu 13 be selected.  The
> generator starting mechanism needs to duplicate the action of a rocker
> switch.  With GLOWSTOP, the relay closes momentarily.  It sounds like the
> relay is remaining closed after starting, when the generator is trying to
run.
>
> Relays 7 & 8 are used for this function.  Relay 8 will start the
generator,
> and then open.  Relay 7 will stop the unit.


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-wrenches mailing list