>QUESTION - To those previous posts that were talking about external
>diversion loads for the air, is there a simple defeat of the internal
>charge regulator, or are you simply cranking the regulator to the max
>and then setting the external load to a lower voltage?

>Kurt Nelson

Kurt,

We are cranking the regulator to max and setting the diversion controller to
a lower voltage.  The AIR Industrial installation manual states that if you
wish to use a diversion controller you must "turn 'off' the internal regular
by gently turning the adjustment screw all the way clockwise."  This sets
the internal regulator to 17.8 volts (35.6V for 24V and 71.2V for 48V
nominal systems).