Voltage drop musings [RE-wrenches]
Windy Dankoff, Dankoff Solar
windy at dankoffsolar.com
Sat May 5 16:37:17 PDT 2001
<x-flowed>
>Hi Windy,
>
>>We sell LOTS of Solar Boost. I have one in my system and have
>>measured 20-25% in winter cold with batteries at about 24.0 V.
>
>Tell me how you are testing to get this figure.
>
>Christopher Freitas was calling into question the way the
>manufacturers calculate it.
OK, yes, it's easy to miscalculate based on the meter in the Solar
Boost, though I'm sure the mfgr is hip to that. The meter can read
battery volts, amps in and amps out. The amps in is at the max power
point, and is thus a bit lower than it would be if directly connected
to the battery (see any IV curve). So, if you calculate the % gain by
dividing amps out by amps in, you reach a falsely high conclusion.
The meter is useful and honest device, just don't misinterpret it.
Instead, here is how I got my gain measurements. I put a SPDT
(transfer) switch on the PV+. In one position it throws PV+ to the
Solar Boost input. In the other position, PV goes straight to the
battery. I compare the amp readings at the battery (shunt to a
Tri-Metric) with Boost in and with Boost out. Simple. As long as
battery voltage is low enough to not cause any regulation of the
charge, you have a comparison of the Solar Boost to the best possible
(zero loss) conventional controller.
Windy
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list