William Miller asked:
> Has anyone on this list researched
>how far one can locate a TM 500 from the shunt and batteries?
I have one where the meter and shunt are 350 ft. apart. I cut the TR500
cable at a junction box about 15 ft. from the shunt, installed a
screw-type terminal strip, and made the long run using #16 AWG (signal)
and #14 AWG (power) to another junction box at the house end, and
connected to the other end of the TR cable. Works fine.
Since the TR cable wire is so small, I stripped double the normal length
to fold-back each wire, doubling the thickness of the wire entering the
term strip.
Installation note: be careful of the shunt orientation. Otherwise you may
have difficulty getting past the 4/0 cables to plug in the RJ-11 cable.
I've done the same with the TriMetric (which licensed their circuitry to
Trace) over distances of 400+ feet. No problems.
Cordially, Chuck
- - -
To send a message:
RE-wrenches at topica.com
Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-wrenches
mailing list