Battery sizing for running the SW [RE-wrenches]
sunwise at cheqnet.net
sunwise at cheqnet.net
Sat Feb 24 15:09:58 PST 2001
> > if maintaining a stable float seems to be a problem at night, maybe it
> > would help to turn the AC1 charging amps way down
>
Doug Pratt wrote:
> That helps, so does turning the absorption volts way down, the float volts
> down, adjusting the float time to minimum, etc., etc. There's lots of
> tinkering you can do to minimize charging wattage,
Hey Doug,
I agree, but actually I wasn't speaking to the issue of attempting to
improve grid-tie efficiency by turning down the charger amps (a whole
nother issue with its own can of worms). I was saying that if you do
put an extremely small battery (200AH) on an SW and leave the charging
amps at the 30A default, the resulting C/6.6 charge rate could have
problems associated with it that go beyond efficiency. -- Kurt Nelson
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-wrenches
mailing list