Battery Bussing [RE-wrenches]
Windy Dankoff, Dankoff Solar
windy at dankoffsolar.com
Fri Aug 31 16:11:28 PDT 2001
<x-flowed>
Joel D said:
>...
>5. Most battery designers limit to 4 or 5 parallel strings by convention.
I would stress the preference of having a single string, them
minimize it, then maximum 4.
>
>I have a question about coating the battery terminals before assembly. Is
>the common recommendation after assembly? I typically have coated after
>assembly and don't coat the AGM's terminals.
>
Travis
There has always been disagreement here, but my reasoning is that
after assembly, you can't get complete coverage to totally seal the
joint, especially on the underside. -- That's the case with anything
of a greasy consistency, like vaseline or copper-containing terminal
compound. If there is a spray product that flows around and then
hardens, then maybe that is effective to apply after.
I don't know the state-of-art, but have seen pre-assembly vaseline
work wonders year after year of no maintenance.
Windy
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list