Grid Tie 240 VAC w/ transfer switch? [RE-wrenches]

Joel Davidson joeldavidson at earthlink.net
Thu Aug 9 07:12:16 PDT 2001


Most of us get together with other designers face-to-face to discuss system
design over sketches, block diagrams and drawings. How can RE-Wrenches
facilitate electronic collaboration on systems like these?

"Bob-O Schultze, Electron Connection" wrote:

> Chris,
> ASSUMING (because you don't say) that your customer wants a manual
> switch (else how would he know he had an outage and to "power down"?)
> and that he has a 200A service, you could put in a manual 200A DPDT
> or 3PDT switch. Two cautions. One, they are a big mother, far bigger
> than a separate service panel, so what's the point? Two, you'll have
> to have the utility power the house down or work getting the feeders
> into the switch hot. Doable, but a little scary. Feeding a dual 60A
> CB and can from the utility side of the switch to the AC1 inputs
> should be no problem IF you can find a way to do it without sticking
> your #6 wires in the same lug as your 200A (probably 4/0 AL) feeders.
> That would work but be a NEC no-no.
> Bob-O
>
> >Dear Wrenches:
> >
> >My client's system is in California; he has two Bergey XL 1's on order, and
> >has two Trace SW4024's and six 120W modules.  He is in a place with rolling
> >power outages and wants back-up (vis a vis eight of the Surrette S460
> >batteries).  His power is rarely out for more than an hour at a time.  His
> >site offers excellent sun and winds, with 15 to 18 mph averages.
> >
> >But, he doesn't want a separate sub-panel for his important loads.  Has
> >anyone done a grid-tie with a transfer switch (located before the main
> >electrical service panel), where one side of the transfer switch is from
> >utility power, and the other leg is 240VAC from the inverter's output?  My
> >client wants total back up not just dedicated loads, and says he'll "power
> >down" in the event of a power failure (and yes, I've cautioned him that if
> >the grid fails, it would be easy to max out his inverters). There is no
> >fuel generator integrated into this system.
> >
> >I've talked with a nice fellow from Asco (http://www.asco.com) about
> >whether their transfer switches would work for this application.  We both
> >think it would--but know of no one who's tested or tried this.
> >
> >One thing I'm uncertain about, code-wise, is feeding the utility input into
> >the AC 1 "in", from the utility side of the transfer switch (like, with a
> >separate 60A circuit breaker).
> >
> >Anybody got any ideas or experience with this type of system?  I'd
> >appreciate any advice you could offer.
> >
> >Chris Daum
> >Oasis Montana Inc.
> >406-777-4321 or 4309
> >406-777-2632  fax
> >http://www.oasismontana.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================







More information about the RE-wrenches mailing list