substitute for Todd battery chargers [RE-wrenches]
Allan Sindelar, Positive Energy, Inc.
allan at positiveenergysolar.com
Mon Apr 23 09:22:09 PDT 2001
Drake, Just a note, with 2 SW4024s and 5 Iota chargers, is your total C/
rate within capacity for the batteries you are using? You will have about
300A input @24V. At about a C/8 max, that takes 2500 Ahrs of battery.
Allan @+E
----- Original Message -----
From: "Drake Chamberlin - Electrical Energy" <solar at eagle-access.net>
To: <RE-wrenches at topica.com>
Sent: Saturday, April 21, 2001 3:34 PM
Subject: Re: substitute for Todd battery chargers [RE-wrenches]
> Hi Wrenches and Doug,
>
> The 24 volt Iota chargers look like they might also be a possible option.
>
> Can you run the Iota battery chargers in parallel? We would probably run
> 5, 25 amp, 24 volt chargers in parallel. They would also be in parallel
> with 2 Trace SW 4024 inverters. We would be using the Iota chargers to
> balance the windings of the three phase generator.
>
- - -
To send a message:
RE-wrenches at topica.com
Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-wrenches
mailing list