Sq D as combiner box [RE-wrenches]
sunwise at cheqnet.net
sunwise at cheqnet.net
Wed Apr 4 17:54:46 PDT 2001
Someone's snip....
"the Heineman breaker will not provide the AIC that
the QO needs--you must use a current limiting fuse"
Eric Smiley wrote:>
> True. There are no current limiting breakers, so a fuse is the only
> option.
Greetings,
I've been following this discussion and I must say that I have
apparently not understood the issue to date. Or, could it be that there
is just some confusion regarding terminology -- Current Limiting vs.
Current Interrupting.
I thought all breakers were current limiting, that is their job, to
limit the current flow on, for instance, a branch circuit. They
typically do not have the current interrupting ratings that fuses in the
R and T class have. A SD fuse will limit the DC current flow to/from a
given device if the amperage begins to exceed the circuits design
limits, like if someone plugged too many appliances ito a circuit with a
conductor protected by a breaker.
They perfom poorly at current interruption, like in a battery based
system when someone sticks a screw driver into a DC branch circuit
outlet box and welds then thing in there good. In such a situation, the
breaker would try to limit the current, but the DC rated/high current
interrupting T class fuse that is protecting the breakers would save the
day.
Could I be way off base here??? -- Kurt Nelson
- - -
To send a message:
RE-wrenches at topica.com
Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9