Wire nuts in DC? was (Re: Fried Combinor Box) [RE-wrenches]
Todd Cory, Bald Mtn. Solar
toddcory at jps.net
Mon Apr 2 11:33:29 PDT 2001
Was that copper or aluminum wire? I regularly find AL wire has "crept" away from
a connection. Sometimes I get service calls for nuisance tripping circuit
breakers and the only problem is a weak (loose) connection that is heating and
tripping the breaker.
Todd
Ray Walters wrote:
> I have personally seen problems with the revered split bolt on DC. Two
> heavy gauge stranded wires together seem to relax over time allowing the
> connections to loosen and corrosion to build. The solution is to clean and
> retighten them, but its hard to even check the connection with the standard
> 1/4 roll of electric tape wrapped around it.
- - -