net metered system question [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Mon Mar 5 13:15:17 PST 2001
<x-flowed>>
> The system has been programmed as follows:
>Trace bulk charge voltage 58.6, Abortion time 2 hours,
>Float Voltage 54.0 (I don't want to set this any higher because the battery
>box vent fans would stay on all the time as they are set to come on at
>54.4v).
David, you don't say what the "sell" voltage is programmed at.
Assuming it is default at 52.8 (I think), what seems to be happening
is very short power outages. Perhaps multiple ones-remember that the
Trace will sense a 16mS outage. After an outage, the Trace will go
into a bulk charge. That will put it off sell for at least the
absorption time of 2 hours. Since the batteries are full anyway, this
would allow the voltage to climb to the 60V (61.9 temp compensated,
would make sense) level then drop to float @55.5 + during that
period. Setting the absorption time to 0:00 would eliminate most of
that.
Bob-O
>Pulse Charge Controller settings: Bulk 60.0 volts, Float 55.5 volts,
>Equalize automatically every 30 days to 61 volts.
> Both the Trace and Pulse settings are temperature compensated.
>The temp comp differential has been running from 1v to 1 1/2 volts (for
>example temp comp volts 54.0, actual volts 55.2v.
>
>PROBLEM: It has been observed, on more than one occasion, (I have not
>re-visited the site yet so I have not personally checked things out yet, but
>a very competent technical person was relaying the info to me via phone
>yesterday),
>that the pv charge controllers were controlling the pv current at float
>voltage,54v temp comp, when observed. The sunlight was strong at that time
>so the sell back that should have been occurring was not happening. After
>the grid sell back was set up (Dec 2000) we had observed good performance on
>sunny days with the meter spinning backwards to the tune of 16 to 20 amps at
>120 volts on each SW4048.
>
>The system monitor (TriMetric) picked up some interesting data that shows a
>recent power outage that could explain at least part of the problem.
>Trimetric high battery voltage 61.9v (Equalized pv actual voltage), and a
>low voltage of 48.5v (this would have had to have been a grid power failure
I think).
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
</x-flowed>
More information about the RE-wrenches
mailing list