Sorry Bill, you are right I neglected to mention that this will be used
as a battery back up for a very critical water bypass valve at the hydro
plant I work at part time.
Last month when the plant went down, the Kohler genny did not start, so
the valve could not open and the river was dry for about an hour... NOT
GOOD and something that FERC SERIOUSLY frowns upon... so I am trying to
come up with a proposal for a battery/inverter based feed system for
this motor.
Suggestions welcome... and I really don't want to try to swap out that
motor to a non 3 phase one unless there is are other options. Everything
at the plant is 3 phase 208.
Isn't interesting how we test this generator every Monday and it never
fails to fire right up.
Todd
- - - - - - -