Drake Chamberlin - Electrical Energy wrote:
>
> Could you say more about the problem with multiple ground paths? With
> wind systems I've been advised to connect a ground rod to each leg of the
> tower.
Yes, that's not a multiple ground path, thats just good grounding of the
tower. I believe these individual tower leg groundings are suposed to
all be bonded as well. An example of multiple ground path on a PV
system would be installing a ground rod at the (pole mounted) array and
bonding the negative leg of the PV to ground at the array, and then
installing a seperate ground rod on the home wiring. Now, you have the
possibility of a voltage potential developing (near-by lightning)
between the two grounds and it is carried through the conductors (and
charge controller, etc.) rather than through the ground wire. Kurt
Nelson
- - - - - - -