<x-flowed>Hi Jay,

I agree that with high voltage systems, extra safety precautions should be 
taken.  Metal conduit would certainly be a good precaution.

On a job I did for Public Service Company of Colorado several years ago, 
the 450 volt, 18 KW system was protected by EMT.  It was a commercial 
building rather than a residence, so no ground fault protection was required.

Best,

Drake ,

At 04:47 PM 02/21/2001 -0800, you wrote:
>Hi Drake,
>
>Thanks for the update.  I bet though that we will see more HI voltage systems
>200v+ and what do you say to the GFI then?  Also with the GFI's built into 
>most of
>the batteryless inverters its not too much of a problem.
>
>But for battery based, yep its a problem.    How about " if wiring is in metal
>conduit from roof to controls then no GFI is needed?  sounds good to me?
>
>later,
>
>jay
>peltz power
>
>Drake Chamberlin - Electrical Energy wrote:
>
> > Hi Jay,
> >
> > I don't know of any proposed changes to the code with respect to the array
> > ground fault protection.  If the RE Lab can get funding, this is one of the
> > areas that we would like to do independent research on.
> >
> > Best regards,
> >
> > Drake
> >
> > At 07:17 PM 02/20/2001 -0800, you wrote:
> > >Hi Drake,
> > >
> > >I agree with you and so have most of the electricans that I have talked
> > >to.  Just
> > >doesn't seem to make electrical sense.  If it opened the circuit at 
> the array
> > >then sure, but like you said, now you have people on the roof to check
> > >equipment-- not good.  No the exsisting equipment doesn't work, its
> > >expensive and
> > >a pain.  I might point out that Both Trace and AEI have the GFI built into
> > >their
> > >batterless inverters, it makes it pretty easy.
> > >
> > >Any chance of getting it removed from the next code?  IS there any
> > >thinking along
> > >those lines.??
> > >
> > >later,
> > >
> > >jay
> > >
> > >Peltz Power
> > >
> > >Drake Chamberlin - Electrical Energy wrote:
> > >
> > > > Hi Wrenches,
> > > >
> > > > The new DC ground fault technology is certainly much better than 
> the old
> > > > Pulse systems.  But I still have a major problem with it.
> > > >
> > > > If the device is to protect the wood framing between the solar 
> modules and
> > > > the charge control, it needs to be mounted on the roof.  If the 
> wire were
> > > > to become shorted (for example with a nail through a cable) the current
> > > > would continue to circulate between the nail and the 
> array.  Heating could
> > > > result, especially with a large array.
> > > >
> > > > A roof mounted ground fault device would likely pose more danger to 
> home
> > > > owners who might climb on the roof to correct nuisance tripping than it
> > > > would eliminate danger from fire.  I suppose a device could be 
> developed
> > > > that would have a reset in the power room and ground fault 
> protection by
> > > > the array.
> > > >
> > > > I believe that better protection could be afforded by using armored 
> cable
> > > > or conduit to protect the circuit.
> > > >
> > > > Have there been any recorded fires from roof mounted arrays?  If there
> > > > really are fire hazards from roof mounted arrays, they should be 
> addressed
> > > > effectively.  I am skeptical about the effectiveness of the current
> > > > technology.
> > > >
> > > > I also doubt that a roof mounted array is as dangerous as a 240 volt
> > > > service drop coming from a pole, capable of delivering 10,000 
> amps.  There
> > > > seems to be a tendency to require RE installations to be 10 times safer
> > > > than grid connected systems.  Why is that?
> > > >
> > > > Drake
> > > >
> >
> > - - - - - - -
> > To send a message:
> >  RE-wrenches at topica.com
> >
> > The archive of previous messages:
> >  http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette:
> >  http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > To unsubscribe send a message to:
> >  RE-wrenches-unsubscribe at topica.com
> >
> > To check out the other RE-Wrench participants:
> >  www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine:
> >  www.homepower.com
> >
> > For info contact list moderator by email:
> >  michael.welch at homepower.com
> >
> > ____________________________________________________________
> > T O P I C A  -- Learn More. Surf Less.
> > Newsletters, Tips and Discussions on Topics You Choose.
> > http://www.topica.com/partner/tag01
>
>- - - - - - -
>To send a message:
>  RE-wrenches at topica.com
>
>The archive of previous messages:
>  http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette:
>  http://www.mrsharkey.com/wrenches/etiquete.htm
>
>To unsubscribe send a message to:
>  RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
>  www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine:
>  www.homepower.com
>
>For info contact list moderator by email:
>  michael.welch at homepower.com
>
>____________________________________________________________
>T O P I C A  -- Learn More. Surf Less.
>Newsletters, Tips and Discussions on Topics You Choose.
>http://www.topica.com/partner/tag01

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01

</x-flowed>



More information about the RE-wrenches mailing list