Windy Dankoff, Dankoff Solar wrote:
> What's it's surge capacity in terms of starting induction motors??
The unit I tested was 12 VDC and was actually loaned to me by a local 
dealer,  so I didn't want to risk damage to it...  There was some 
clipping of the AC output sinewave already with a 2000 watt AC load, 
suggesting it was already starting to current limiting .  They list 5000 
watts as the surge but I am not sure how they came up with that - no 
maximum AC current spec is provided.  This may be able to start up a 
large motor,  but the SC output voltage will drop severely during the 
process,  risking problems (and even damage)to any other loads operating 
at the same time. 
I would suspect that the 24 vdc unit would work better in the real world 
for starting motors.  When I get my hands on one I will let you know 
what I find out.  
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  
www.outbackpower.com
Tel 360 435 6030  
Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
    
    
More information about the RE-wrenches
mailing list