<x-flowed>Hey Jay The voltage drop/wire size problems that would be encountered pose
a cost problem even @220 vts.Another thing that having a fuse/breaker box
at the pole is that if batteries were shut off ,when the inverter was
reconnected the charge rate would be 30 amps ac(default setting). Unless
you had a 250 awg @ 110vts and breaker to anticipate this then it would
trip the breaker at the pole unbeknown to the customer.The "AC 1" light
would blink the customer might think that they are still getting a grid
charge and possibly have the system shut down due to low batt voltage. Seen
this situation happen w/ undersized generators and poorly educated
customers.Where you are its a long trip to reset the parameters.Good $$$
long ride!
- - - - - - -