RE Lab Experiment #1; BATTERY CABLES; Preliminary Results [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Sat Mar 11 13:59:25 PST 2000
<x-flowed>Hi Wrenches,
Early results from the ACID TEST of various cables, which might
be considered for battery connections, are now in. All cables have
been in solution for at least a week at this point.
CABLES TESTED:
2/0 AWG THW OR OIL RESISTANT I 600 V E70347 Made in Canada From Bob-O Schultz
2/0 ESSEX EXCELENE WELDING CABLE from Bob-O Schultz
4/0 COBRA WIRE & CABLE X-FLEX E163983 (UL) MTW OR THW OR AWM 600V,
105 DEGREES C (TRACE CABLE) from Quicksilver Electrical
4/0 CAROL PRENE WELDING CABLE 600V from Quicksilver Electrical
4/0 CAROL SUPER VU-TRON TYPE W PORTABLE POWER CABLE RHH OR RHW 90
DEGREES C DRY 75 DEGREES C WET 2000 V from Quicksilver Electrical
2/0 HYPALON DIESEL LOCOMOTIVE CABLE IEEE 383 --- CSA AWM 8A 90C 600V
FTI TYPE USE OR RHH OR RHW FOR CT USE VW-I A.I.W. CORP from
Electrical Energy
2/0 ESSEX THHN OR THWN 600V from Quicksilver Electrical
RESULTS:
The only cable to show any visible signs of deterioration is the
THHN / THWN. The battery acid became dark and discolored within a
day. Well before the end of a week, the solution became so dark that
the cable sheath within was difficult to see.
The THHN / THWN sheath was taken out of the acid for examination.
It appears to be losing mass, but is still in tact. The sheath will
go back into the solution.
None of the other cable has shown any visible signs of
deterioration. The battery acid for the other samples have shown no
signs of discoloration.
WHAT IS IMPLIED
The implications, at this point, are that welding cable seems to
hold up as well to acid as the cables that are presently approved for
use in battery boxes. The THHN / THWN cable, which is not approved,
and is not particularly popular for use as battery interconnects, has
the least suitable insulation of the cable sheaths tested.
The cables will be allowed to soak for a longer period. After
this period, the cables will be subjected to testing with a mega ohm
meter (Meggar) to determine if there is any loss of resistance to
applied voltage.
REMARKS
It is probable that the tested insulation has already been
subjected to more acid contact than a cable in a battery compartment
would be during its entire period of use.
Many approved cables have pure copper conductors within the
insulation. The difference between the various cable is therefore
mainly in the insulation. Although stranding size may vary, finely
stranded cable is approved for use in battery compartments, even
though fine strands are more susceptible to deterioration.
The insulation on THHN / THWN wire demonstrates a susceptibility
to acid, and would probably be the least suitable for use in battery
boxes.
Coincidentally, yesterday we went on a site visit to an existing
system. The battery jumpers were made from type THHN cable. They
seemed to be in excellent shape. The actual amount of acid contact
with cables in battery boxes is likely to be small.
The CAROL SUPER VU-TRON TYPE W PORTABLE POWER CABLE RHH OR RHW is
a cable that has been accepted for use in battery compartments under
current regulations. However it has an extremely thick sheath and is
very awkward to work with. It is difficult to get two of these
cables into 2" Schedule 80 PVC conduit.
The experiment is not complete. These findings, although
preliminary, demonstrate that no catastrophic results occur when
welding cable is exposed to battery acid.
Drake Chamberlin
Electrical Energy
(303)399-1025