One EMP and we'll all be clamoring for FLA's again. Hope it never comes to
that my friends.
Christopher
On Wed, Jun 17, 2026 at 6:13 PM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Chris
>
> The key is exactly what voltage, current and for how long.
>
> I’ve had a few cells fail over the years usually not my customers, and I
> think all but 1 was customer screwup. Wrong charge voltage, time not enough
> amps etc. and not testing via specific gravity and volts.
> but 1 was a true failure.
>
> The fall of lead has been faster than I expected.
>
> Jay
>
>
>
>
>
> On Jun 17, 2026, at 2:54 PM, Chris Daum via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Yes, I’ve been selling these since 2007. Damn good batteries; I did hear
> from Tommy in a roundabout fashion; THE contact person at Enersys is Jammie
> Bednarek, 484-203-8660, and her e-mail is jammie.bednarek at eversys.com.
> If you have a bunch of these batteries out there, take note!
>
>
>
> And thanks for your input.
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
> 406-777-4309
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Ray Walters via RE-wrenches
> *Sent:* Wednesday, June 17, 2026 12:33 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Cc:* Ray Walters <ray at solarray.com>
> *Subject:* Re: [RE-wrenches] Solar One HUP batteries
>
>
>
> We were a distributor for the HUP Solar One for almost 2 decades.
> Enersys, the parent company, decided to pull the plug on the entire HUP
> line, due to reduced demand for lead acid batteries, and then the 2025
> Tariffs were the final blow. We were told to pull all advertising, and
> mention of what was a great battery. I don't know what to say about a
> replacement cell, other than to contact Enersys directly and try to work
> through the chain of command.
>
> Tommy retired with that, so is no longer a contact point, and I really
> don't have anything to offer either. A bad cell is highly unusual with the
> HUPs, I only saw that on a system where the owners were not able to get to
> one of the cells, and so it went dry. I've recovered cells by charging
> them vigorously with a large automotive charger set to 6 v, and just put
> that across the terminals of the individual cell while charging the whole
> system as well.
>
> Also, the HUPs need a pretty high charge rate to bring the cells to full
> SG. Depends on the model, but the minimum charge rate can be as high as 200
> amps for the largest model. I've attached a spec sheet with minimum charge
> rates listed. Basically if you aren't getting close to those charge rates,
> you can end up with sulfation damage long term. I've almost always been
> able to recover HUPs, but it might take 2 days of EQing at very high
> voltages (62 v @ 48v nominal) nothing will happen, and then finally the SG
> will start moving.
>
> Ray Walters
> Remote Solar
>
> On 6/17/2026 11:59 AM, Dana Orzel via RE-wrenches wrote:
>
> Chris I am on the Solar One If no reply let em know I can dive into my
> battery box & look at ID & Data
>
>
>
>
>
> _________________________________________________________
>
> Dana Orzel GREAT SOLAR WORKS!
>
> C – 208.721.7003 E – dana at solarwork.com
>
> W - www. greatsolarworks.com www.solarwork.com
>
> *“Responsible Technologies for Responsible People since 1988!”*
>
>
>
>
>
> _______________________________________________
>
> List sponsored by Redwood Alliance
>
>
>
> Pay optional member dues here: http://re-wrenches.org
>
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
>
> Change listserver email address & settings:
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>
> There are two list archives for searching. When one doesn't work, try the other:
>
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>
>
> List rules & etiquette:
>
> http://www.re-wrenches.org/etiquette.htm
>
>
>
> Check out or update participant bios:
>
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Chris Schaefer’s
*Tel 585-229-2083 or Cell 585-748-1870 *
*5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*
Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260617/58696b1e/attachment.htm>
More information about the RE-Wrenches
mailing list