[RE-wrenches] Ev charger off grid
David Quattro
david at quattrosolar.com
Wed Jun 3 10:30:35 EDT 2026
The solution in our case was to shine up all the copper ground wires and
tighten ground connections - everything from the electrode back to the
inverter, and to the EV charger.
*David *
On Wed, Jun 3, 2026 at 6:58 AM Chris Sparadeo via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Jay,
>
> Most leve 2 EVSE do not require a neutral wire and come with internal GFCI
> protection. It’s best to hardwire the charger to avoid additional GCFI OCPD
> requirements and potential nuisance tripping that come along with NEMA
> 14-50 plug in installations.
>
> On Wed, Jun 3, 2026 at 9:34 AM Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> And what if the charger doesn’t have a neutral, just a ground?
>> Does the same issue apply?
>>
>> On Jun 3, 2026, at 7:14 AM, Tyrone Houck via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>>
>> I have seen chargers cause afci/gfci fault errors off grid when there
>> were redundant neutral bonds and scenarios where a better electrode was
>> needed. In my experience car chargers are sensitive to needing a solid
>> ground connection.
>>
>>
>>
>>
>> On Wed, Jun 3, 2026, 6:05 AM Jay via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hi all.
>>>
>>> I have someone with a SOL ark 12 (9kw max offgrid) who hooked up a EV
>>> charger and it’s now tripping ac dual arc/gfi breakers.
>>> I figure the charger or car or both are making noise and the breakers
>>> trip.
>>> The charger is set to 16 amps.
>>>
>>> I guess my question is since this doesn’t happen on grid, or at least I
>>> never hear about it, is this an issue anyone has seen in other offgrid
>>> install?
>>>
>>> Thx
>>>
>>> Jay
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260603/d43a74c3/attachment-0001.htm>
More information about the RE-Wrenches
mailing list