[RE-wrenches] Balcony Solar
Jason Szumlanski
jason at floridasolardesigngroup.com
Fri May 29 07:55:50 EDT 2026
Somebody coined the term "breaker masking" for this issue.
https://floridasolardesigngroup.com/is-plug-in-solar-safe-the-wiring-danger-that-marketing-will-not-tell-you-about
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Thu, May 28, 2026 at 3:55 PM Zeke Yewdall via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Yes... if the PV is not on the last outlet in the string, there is the
> potential for overloading a portion of the string if someone plugged in
> more than 16A of heavy loads farther out on the string -- the wire portion
> between the PV backfeed and the next outlet could have more amperage on
> it. Same issue as when your backfed breaker isn't on on the opposite end
> of the busbar from the grid feed.
>
> I remember the OK4U inverter from Trace. Back when mechanical meters just
> spun backwards. It was discontinued before I ever lived somewhere with
> grid power, so never got to use one.
>
> Then they started putting electronic readers on the mechanical meters, and
> they only counted how many times the black line went by, not which
> direction, so were effectively ratcheted, and I believe all of the standard
> electronic ones now are ratcheted in the software. Or, they're smartmeters
> that immediately report back if you sell a few watts ever. I've seen
> people run into that numerous times when self consumption systems blipped
> below 0 watts during load changes, when the inverter wasn't programmed for
> enough baseload draw from the grid.
>
> On Thu, May 28, 2026 at 12:27 PM Bryan Norkunas <bryan at pv-cables.com>
> wrote:
>
>> Was this considered balcony solar back in 1998?
>>
>> Bryan Norkunas
>> PV-Cables, Inc.
>> 989 Milton Ave Ste 1-D
>> Ferndale, CA 95536
>> 707-923-3000 office
>>
>> ------------------------------
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>> behalf of Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Sent:* Thursday, May 28, 2026 12:10:27 PM
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Cc:* Jay <jay.peltz at gmail.com>; Zeke Yewdall <zeke at darkforestsolar.com>;
>> RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] Balcony Solar
>>
>> Hi Zeke
>>
>> I see a few issues.
>>
>> If there is a circuit with A as the first outlet then B,C,d. If the 16A
>> is put into B then C and D now have the potential for 36 amps. Bit high for
>> 12 ga wire.
>>
>> As to the meters as far as I know most all meters unless configured for
>> bidirectional use either are mechanical ratcheting so they cant count
>> backwards. Or are electronic and I’m unclear as to what happens. I e heard
>> they count up either direction so if your selling power the meter adds or
>> it might just lock like the ratcheting. I guess depending on the meter.
>>
>> Finally I live in an all electric house and for most of the year, 8+
>> months when I’m not using heat, my daytime base loads are like 200 watts.
>> Of course if someone is home then could be laundry etc.
>>
>> A small system say 400 watts or less is going to be mostly used for some
>> daytime self consumption. But 2000 watts is way overkill and for most it
>> seems it will be wasted for the consumer. And as you say it’ll make people
>> mad about how little it’s doing.
>>
>> Finally as to dates. I had a OK4U made by NKF back in 2000 grid tie micro
>> inverter for a single 100 watt panel plugged into an outlet on my deck. I
>> keep reading it’s a new idea, nope.
>>
>> Big push lots of hype.
>>
>>
>>
>> On May 28, 2026, at 9:40 AM, Zeke Yewdall via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>> Trying to wrap my brain around exactly what this entails. Specifically
>> in Colorado, as that's where I still do most of my design work, but also in
>> other places if it's different/better/worse/etc....
>>
>> This is the actual text of the Colorado bill
>> https://leg.colorado.gov/bill_files/116074/download
>>
>> From reading it... it appears that it's limited to 1920 watts AC output,
>> and limited to one system per address. Systems under 391 watts AC output
>> are exempt from a number of other requirements (which seem to pertain
>> mostly to NABCEP certified supervisors and licensed electricians), but
>> still have to be UL listed. Does that imply that licensed electricians or
>> NABCEP certified installers must install ones between 391 watts and 1920
>> watts?
>>
>> It appears that utilities cannot require approval, a fee, or any
>> modifications to the house electrical system (4a) but can require being
>> notified of the installation and size (4b)
>>
>> I am wondering how this works with ratcheted meters, which is the norm
>> nowadays in Colorado. I have asked Xcel for their guidance on this.
>>
>> In general... the idea of balcony solar seems very problematic. While
>> I'm totally in support of more solar on the grid, and making smaller
>> systems more doable, I have lots of questions on how this will work in
>> reality.
>>
>> 1) Structural issues: Most homeowners do not know how to properly mount
>> solar panels against the winds that we have in Colorado. It's normal for
>> cars and neighbors to be assulted by wandering trash cans during every
>> windstorm... adding errant solar modules to this doesn't seem like a good
>> idea. Most temporary solar racking I've seen from manfucturers (from RV
>> solar sellers mostly) is completely inadequate to withstand 100+mph winds
>> as well. How will proper securing of the solar modules be enforced?
>>
>> 2) Electrical integration: 1920 watts is a fully loaded 20A 120 volt
>> output (16A continuous). If it is a new, high quality outlet, it should be
>> good for that, but what if it is a old outlet on the deck that's gotten all
>> loose from 30 years of power tools and christmas lights being plugged and
>> unplugged? What if it's the $1.99 consumer version of the outlet, not the
>> $8.99 commercial version? I've seen the cheaper ones, and many old loose
>> ones, burn up when used with electric space heaters, which is a similar
>> amperage and time span load to a full size balcony solar system.
>>
>> 3) Metering: Since most all utilities in Colorado now use ratcheted
>> meters, it will be a problem if the system exports without somehow getting
>> a bidirectional meter. If it is a lightly loaded apartment, where a 1920
>> watt system would really make a different in energy use, then it's likely
>> the baseload will be below 1920 watts midday, and it needs to export. If
>> it's a larger house where the baseload midday is over 1920 watts, then
>> export isn't the issue, but the problem is that people will install a 1920
>> watt system when they really need a 5 or 8 or 12kW system to affect their
>> bill much -- and then they'll just decide that "solar doesn't work" and it
>> will give solar a bad name for more people. Given that most people don't
>> understand kWh and energy use, and marketing always seems to overpromise
>> what equipment can do, I don't expect that a majority of consumers will
>> understand that a 1920 watt system is not sufficient to make a significant
>> impact for a majority of houses out there. I've even had customers install
>> 10kW systems, and not understand that by adding a hot tub and electric
>> water heater and heat pump and electric range at the same time, they
>> overwhelmed the production of the system, and that's why their bill
>> actually went up.
>>
>> 4) Licensure and permits: This could solve some of the issues above...
>> but Colorado allows homeowners to pull permits so licensure and training of
>> the installer is still no guaranteed. And most building departments have a
>> permitting process that's aimed at larger systems... a large system
>> requiring 10 pages of documentation and an engineers stamp and a $500
>> permit fee is not unreasonable. But for a $2000 balcony kit... how can
>> permitting enforce some basic standards, without becoming a insurmountable
>> hurdle. Also, as a professional installer, I found that fixed costs were
>> a large portion of the cost of installing a system. My cost to do
>> drawings, get a PE stamp for the roof/racking, file for a permit, file for
>> interconnection agreement, and roll a truck were pretty much the same for a
>> 3kW system or a 10kW system. There was more onsite labor for the 10kW
>> system doing racking and modules, but even electrical wiring was about the
>> same onsite labor for both sizes. Onsite labor should be much less for a
>> balcony solar system, especially if plugging into a deck outlet (replacing
>> it with a brand new commercial quality 20A outlet maybe). But costs for
>> drawings, permitting, interconnection won't be different unless a different
>> system is made. Materials are obviously more for the larger systems, but
>> labor made the overall total cost quite a bit higher per watt for the
>> smaller systems, and going to a one or two panel system could be even more
>> share for the off-site labor portion of the total cost. If building
>> departments and utilities put the balcony solar systems through the same
>> paperwork as larger systems, I can easily see that costing more than the
>> materials or onsite labor.
>>
>>
>>
>> --
>> Zeke Yewdall
>> PV Engineer
>> NABCEP #031508-89
>> zeke at darkforestsolar.com
>> 303-523-3592
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
> Zeke Yewdall
> PV Engineer
> NABCEP #031508-89
> zeke at darkforestsolar.com
> 303-523-3592
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260529/a21d40b1/attachment.htm>
More information about the RE-Wrenches
mailing list