[RE-wrenches] Combiner breakers tripping
All Solar
allsolarpenrose at gmail.com
Fri May 1 17:47:05 EDT 2026
Jay and all,
Here are the details you requested, from the module nameplate (I have not
tested these yet):
- Breaker Size: 9A
- VOC: 41.2V
- VMP: 32.9V
- IMP: 3.34A
- ISC: 3.69A
- Max Series Fuse: 20A
- Configuration: One module per string feeding a SB50 charge controller.
- 10 or 12 guage wire from modules to combiner
-Breakers are approximately 20yrs old
Jeremy Rodriguez
All Solar Inc.
Penrose CO
719-276-4954
Established 1998
On Fri, May 1, 2026 at 6:21 AM Jay <jay.peltz at gmail.com> wrote:
> Pls tell us
> Size breaker
> Voltage input
> Amperage input
> Wire size
> Age of breakers
>
> Thx
>
> On Apr 30, 2026, at 10:31 PM, All Solar via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Wrenches,
> I've got a c client with an Outback PV combiner with DIN mount CBs. He's
> let me know a few times that 9 of 10 , or at least 50%
> of the breakers are tripping for no apparent reason. He resets, and all is
> fine for a few months.
>
> I suspect something is wrong with the array vs. the breakers needing
> replaced.
>
> What should I be looking for and checking?
>
> The client has made sure the breaker screws are tight.
>
> - Off grid
> - Pole mounted array
> - Solarex 110 w Modules
>
>
>
>
> Regards,
>
> Jeremy Rodriguez
> All Solar
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260501/4bc28ef1/attachment.htm>
More information about the RE-Wrenches
mailing list