[RE-wrenches] Combiner breakers tripping
Ray Walters
ray at solarray.com
Fri May 1 17:22:54 EDT 2026
I know, but I think Outback possibly had a bad batch about 20 years
ago. They were tripping just a year after installation....
Ray
On 5/1/2026 3:20 PM, jay wrote:
> They are both made by CBI of south africa
>
> I’m wondering if age is the main issue?
>
>
>
>> On May 1, 2026, at 3:08 PM, Ray Walters via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> I've also seen some Outback 15A breakers in combiner boxes just trip
>> when they shouldn't. Replaced with Midnite and quit having
>> problems. As others mentioned, going to larger breakers is usually
>> fine. I usually match the fuse rating for the module itself. Many
>> are 20A, which gets away from any edge of cloud stuff too.
>>
>> Ray Walters
>> Remote Solar
>>
>> On 5/1/2026 1:55 PM, David Coale via RE-wrenches wrote:
>>> It could be that the breakers are tripping due to the cloud-edge
>>> effect. This happens when you have a sunny day with a few puffy
>>> clouds drifting by. As the clouds start to shade the array, there
>>> is a focusing effect around the cloud that will increase the
>>> sunlight on the array. If the breakers are close to the max output
>>> of the array, then they can trip during these sunny/cloudy days.
>>> Increasing the breakers to the next size up, if the wiring will
>>> handle it, will fix the problem. I have seen this in a few
>>> installations. Changing the breakers from 10 amps to 15 amps fixed
>>> the problem.
>>>
>>> David
>>>
>>>
>>> On Thu, Apr 30, 2026 at 9:31 PM All Solar via RE-wrenches
>>> <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> Wrenches,
>>> I've got a c client with an Outback PV combiner with DIN mount
>>> CBs. He's let me know a few times that 9 of 10 , or at least 50%
>>> of the breakers are tripping for no apparent reason. He resets,
>>> and all is fine for a few months.
>>>
>>> I suspect something is wrong with the array vs. the breakers
>>> needing replaced.
>>>
>>> What should I be looking for and checking?
>>>
>>> The client has made sure the breaker screws are tight.
>>>
>>> * Off grid
>>> * Pole mounted array
>>> * Solarex 110 w Modules
>>>
>>>
>>>
>>>
>>> Regards,
>>>
>>> Jeremy Rodriguez
>>> All Solar
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't
>>> work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here:http://re-wrenches.org
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260501/f03624c9/attachment.htm>
More information about the RE-Wrenches
mailing list