[RE-wrenches] Sol-Ark 15K2P F20 MPPT Overcurrent Error

Vince McClellan vince at solarenergydesign.com
Fri Apr 10 22:01:12 EDT 2026


Hi David
I appreciate your help. I hadn't thought of swapping strings because the
MPPT channel that is triggering the F20 error is always different. It could
be worth a try anyway as it's easy to do. I do think we're down to swapping
the inverter to see if that clears the issue.

Sol-Ark hasn't been much help on this one.

Have a great weekend,


Vince McClellan

President

NABCEP PV Professional

p: 541-485-8122

a: 860 Conger St. Suite 12,. Eugene, OR 97402

e: vince at solarenergydesgin.com

w: SolarEnergyDesign.com

CCB# 161672

If you have received this email and are not the intended recipient, please
delete this email. Copying or using any part, content, or attachment of
this email is strictly prohibited.


On Fri, Apr 10, 2026 at 4:54 PM david quattro <david at quattrosolar.com>
wrote:

> i would swap which strings go into the different MPPT's to see if each
> specific problem follows the DC string // or do they follow the MPPTs.
> Another option is kinda a lot of work but might be worth it - take a
> different inverter out there and "bench test" it with those strings
> unadulterated
> Good luck and please let us how this one resolves.
>
>
>
> On Fri, Apr 10, 2026 at 4:05 PM Vince McClellan via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hello Wrenches
>> Has anyone else on this list had issues with a Sol-Ark 15K2P randomly
>> shutting down several times a day with an F-20 MPPT overcurrent error? The
>> errors are occurring when the system is well under the max amperage per
>> MPPT of 26 amps. We've had the inverter turn itself off when the online
>> data shows 12.5 amps max. I realize that Sol-Ark's online data updates only
>> every 5 minutes, so I could be possible that there is a spike that the
>> online data isn't showing, but the array is in full sun with the same
>> number of modules and the same string configuration on all 3 MPPT's.
>>
>> We are also seeing other anomalies such as MPPT 1 at 12 amps with MPPT 2
>> and 3 at 22 amps. Again, with the solar array in full sun, no clouds, and
>> no shade.
>>
>> Sol-Ark originally thought it was because of an issue with Tigo RSD
>> switches, but we don't use Tigo. We've had way too many issues with Tigo
>> products.
>>
>> We've had people suggest that we're seeing the results of an edge of
>> cloud affect, but there are not clouds to cause this.
>>
>> We've also tested all the circuits with a insulation tester in every
>> possible configuration, and tested our wiring to insure there were no
>> mistakes by ringing it out with a multimeter. The wiring is good.
>>
>> Sol-Ark tech support doesn't seem to know what the issue is, but they are
>> assuring us that it's not their inverter at fault.
>>
>> I could use any suggestions that come to mind. I'm not sure what else to
>> try at this point.
>>
>> Thank you,
>>
>>
>> Vince McClellan
>>
>> President
>>
>> NABCEP PV Professional
>>
>> p: 541-485-8122
>>
>> a: 860 Conger St. Suite 12,. Eugene, OR 97402
>>
>> e: vince at solarenergydesgin.com
>>
>> w: SolarEnergyDesign.com
>>
>> CCB# 161672
>>
>> If you have received this email and are not the intended recipient,
>> please delete this email. Copying or using any part, content, or attachment
>> of this email is strictly prohibited.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260410/12bbcb5e/attachment.htm>


More information about the RE-Wrenches mailing list