[RE-wrenches] Portable power station for surge loads
Corey Shalanski
coresolar at gmail.com
Sun Mar 22 22:06:17 EDT 2026
Hi Ray,
RE. the *NEC* Chapter 9 Table 8 resistance adjustment formula: I believe
temperature T2 is the operating temperature of the conductor - not
necessarily ambient temperature... unless I'm mistaken?
Corey Shalanski
Jah Light Solar
Portland, Jamaica
On Sat, Mar 21, 2026 at 7:20 PM Ray Walters <ray at solarray.com> wrote:
> I remember doing some measurements on a long wire run, and being surprised
> that the actual voltage drop was much less than the calculations. That's
> when I found a small note at the bottom of the NEC Table 8 conductor
> properties used for official VD calculations. The resistance is listed at
> 167 F (75C), so if you use the adjustment equation in Note 2, it is much
> less VD, and corresponds to reality. For underground conductors, I might
> use 25C. Use common sense.
>
> The formula is R2=R1 (1+ a(T2-75))
>
> I made a spread sheet about 15 years ago, that uses that formula for doing
> wire sizing. Happy to share, if anyone is interested.
>
> Ray Walters
> Remote Solar
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260322/66492e88/attachment.htm>
More information about the RE-Wrenches
mailing list