[RE-wrenches] Outback FXR Slaves Not Charging With AC

Steve Higgins steve at surrette.com
Mon Mar 16 10:49:21 EDT 2026


Hey Jason... I'll admit it's been awhile since I was with OB.   But from
what I remember you can only have one Master inverter.

You can't have a master and slave on each leg.

The port one inverter needs to be a 1 -2 phase master.

The other three should be slave L1 or L2 depending on the phase that they
are connected to.

My bet is the charging isn't syncing due to the master/slave setup.

Right now they aren't backfeeding due to the generator is syncing the
phases.  I like to call magic stacking.    Eventually when the generator
isn't running you could see enough drift from that 2nd 1-2 phase master
that might cause a backfeed or overcurrent error.


*Steve Higgins* *⋅* *Technical Services Manager*
*t* +1.902.597.4020   *m* +1.206.790.5840
*f* +1.902.597.8447   *e* steve at surrette.com
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------



On Mon, Mar 16, 2026, 7:40 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> I inherited am off-grid service client with four FXR3048A configured in
> 120/240 split phase with one master and one slave per leg. I believe I
> configured all of the AC input charging parameters correctly, requesting
> max charge rate from each inverter. However, when AC input is present (from
> a generator) the masters will bulk charge, but the slaves do not charge at
> all. The slaves do share the load, but show 0.0kW for charging.
>
> Any ideas?
>
> Jason Szumlanski
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260316/a54da212/attachment.htm>


More information about the RE-Wrenches mailing list