I like the ingenuity, Jason. I would assume you would still need to CT the
other half of that 320A service for whole site monitoring requirements. If
the total service is pulling more than 160A I am wondering if the PCS would
try to limit battery charge/discharge to prevent overload on what the EMS
is thinking is a 200A bus bar. To be fair, that would be quite a load, even
on a 320A service…
On Thu, Feb 5, 2026 at 6:25 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I had a thought. What about just backing up one of the two 200A panels
> with an off-the-shelf residential MID, and install an automatic transfer
> switch on the other 200A panel with the primary source being the grid, and
> auxiliary source being the inverter output, possibly through a feeder from
> the first 200A panel.
>
> This would allow backup of all loads on a single 200A MID. I would comply
> with 710.15(A) (NEC 2020) without any required load management.
>
> Better yet, make the auxiliary source for the second 200A panel a feeder
> from a smart load breaker in the MID for load management purposes. The EG4
> GridBOSS can send a 125A feeder to the other panel. That would be more than
> sufficient for practical purposes in a grid outage.
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
> On Thu, Feb 5, 2026, 8:48 AM Jay <jay.peltz at gmail.com> wrote:
>
>> I reread your question.
>>
>> I think the only way to be sure the internal transfer switches in the
>> inverters all switch at the same time on a big high load ( exceeding
>> potentially the max current rating of a single relay) multi stack inverter
>> system is to use external transfer switch’s.
>>
>> The system I installed is never going to exceed 200 amps, probably never
>> exceed 80 amps. 2 inverters can more than handle the load. The 3rd was
>> installed as built in redundancy to make it easier in case one fails. As
>> the system won’t run on 1. So I didn’t have to worry about exceeding relay
>> capacity.
>>
>> I think this is one of the potential problems with paralleled systems vs
>> larger single 120/240 inverter’s which we don’t really have here in the US.
>>
>>
>>
>> On Feb 4, 2026, at 7:05 PM, Jay <jay.peltz at gmail.com> wrote:
>>
>>
>> I have a 3 stack eg4 18k and while watching the inverters online they are
>> totally balanced.
>>
>> Jay
>>
>> On Feb 4, 2026, at 4:29 PM, Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>> Hi all,
>>
>> When backing up a 400A service with multiple paralleled all-in-one
>> inverters by combining the AC inputs and outputs, the individual inverter
>> transfer switches must operate in a synchronized manner. Come to think of
>> it, the same thing applies to backing up 200A service with paralleled
>> inverters. Are these tested for this function? – I assume so.
>>
>> I'm really asking because Sol-Ark seems to be the only brand that
>> specifically addresses 400A service in documentation, although not very
>> clearly in the manual itself. Their training and literature support passing
>> through additive grid pass-through with multiple inverters, which implies
>> that they are additive in their ability to transfer power. See attached
>> examples.
>>
>> I have not found anything from EG4 (for the 18kPV) or the Midnite AIO
>> that specifically addresses this.
>>
>> In other words, how can we assume that paralleled inverters will be
>> additive in terms of their ability to transfer high levels of current that
>> exceed the rating of a single unit? Is that even addressed in listings? The
>> documentation is quite poor from all manufacturers (no surprise there!)
>>
>> I do have a couple of grid-interactive Midnite AIO systems with four
>> paralleled AIOs backing up 400A services, and so far, so good. My engineer
>> signed off on that.
>>
>>
>> Jason Szumlanski
>>
>>
>> * <http://www.floridasolardesigngroup.com/>*
>> <Image 1171.jpg>
>> <Image 1172.jpg>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260205/f64f4b57/attachment.htm>
More information about the RE-Wrenches
mailing list