A guess is too many devices on the xanbus. Are you using Facility?  The 
-60 reverting is a new one for me. Maybe isolate each one seperately in 
case one is malo.

buenas suerte!

Dave Angelini Offgrid Solar
"we go where powerlines don't"
    [1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2026-01-13 4:29 am, Jason Szumlanski via RE-wrenches wrote:

> I have a new client with an existing Schneider dual XW Pro system with 
> four MPPT 100 and two MPPT 60 charge controllers. They have a SCP, AGS, 
> and Insight.
> 
> The system is reporting DC over voltage faults on the two inverters 
> (viewable via SCP. The battery voltage is not high. It's a bank of EG4 
> LL batteries that would hit their high battery cutoff well before the 
> XW detects a high battery condition.
> 
> I went through all of the setting and discovered that the two MPPT 60 
> were set to a nominal voltage of 36V. I fixed that by changing them to 
> 48V and cleared the faults and all was well. I did this though the SCP.
> 
> By the time I came home, however, the faults returned and the MPPT 60 
> both reverted to 36V nominal.
> 
> I'm not sure why the DC over voltage faults are showing up on the XWs, 
> but it seems related to the nominal voltage issue on the MPPT 60s.
> 
> Any ideas?
> 
> Schneider tech support has me wasting time today going for a boat ride 
> to the site to put a meter on the battery terminals, when I know it's 
> obviously not an actual battery voltage issue. I'm hoping to steer them 
> in a different direction.
> 
> Jason Szumlanski
> Florida Solar Design Group
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org


Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20260113/72e1b21c/attachment.htm>


More information about the RE-Wrenches mailing list