Transformer T240 [RE-wrenches]

Michael Welch michael.welch at homepower.com
Mon Aug 10 12:45:57 EDT 2026


<html>
At 11:16 AM 03/23/2000 -0800, you wrote:<br>
&nbsp; <br>
<blockquote type=cite cite>2) the Trace T240 is rated for 3900 watts continously. You're pushing its limits with a 4600 watt generator.<br>
<br>
I'd recommend a larger generator (6 kw) min. At least you'd have 20 minimum available amps for household loads if the Trace charger were operating at maximum ouput of 30 amps([6000 watts /120 vac] - 30 = 20 amps). You'll have to use a larger transformer for step down than the T240. Call me if you're interested in finding a source.</blockquote><br>
AEE has &quot;Autotransformers&quot; in NEMA 1 enclosures, 98% efficient, &lt;0.2% no load idle loss, quiet. 2.5, 4, &amp; 8 kw.</html>