[RE-wrenches] VFXR3648A battery charging
William Miller
william at millersolar.com
Sat Dec 13 16:09:04 EST 2025
Jay:
Thanks for that. I always thought re-bulk only applied if you had 24/7 AC
input which we do not. I made the adjustment and we will see what happens.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Jay [mailto:jay.peltz at gmail.com]
*Sent:* Saturday, December 13, 2025 12:11 PM
*To:* william at millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] VFXR3648A battery charging
You have to set the rebulk volts higher, higher than what ever you start
the generator.
Say 56 or so.
Jay
On Dec 13, 2025, at 11:56 AM, William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
Friends:
I have a client with one VFXR3648A inverter off-grid with PV and a
generator. The inverter is set to bulk at 58.2 VDC for 2 hours but when
the generator is required the voltage never gets above 52 VDC. The PV gets
the voltage up to the 58 volt zone reliable.
The original generator was a portable of about 3 Kw. I thought it was not
providing enough RMS power so we upgraded to a Kohler vertical shaft 12 kW
air cooled unit. The problem is still the same: The bulk voltage of the
batteries never gets above 52 VDC.
On my next visit I plan on resetting the inverter to factory defaults.
Other than that I am not sure what to try. I have little luck reaching
Outback tech support in the last year so I am hoping someone here can
provide some advice.
Thanks in advance.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251213/657be5ab/attachment.htm>
More information about the RE-Wrenches
mailing list