[RE-wrenches] 2KW PCS import/export limit on a 25KW transformer; Oncor in Texas

Dave Tedeyan dave at sungineersolar.com
Wed Nov 26 10:59:20 EST 2025


If Oncor is anything like my utility here in NYS, they have a 25kwAC export
limit. The utility here will count anything that can potentially export
some amount of power towards that limit. For example 4 kw of solar on an
8kw inverter counts as 8kw towards the limit. Maybe you can tell them that
the batteries will not export anything? And at least in NY if other
customers are on the same transformer, they are not allowed to charge for a
transformer upgrade.
Good luck!

On Wed, Nov 26, 2025, 9:57 AM scot.arey--- via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> In my 13 years installing solar in Texas, I've never had a utility come
> back and say "you must set a PCS limit of 2KW through this 25KW transformer
> or you can pay to upgrade the transformer."
>
> System is 12KW of solar (9KW AC equiv.) and 6x Enphase 5P batteries (23KW
> AC) so total of 32KW of potential power export if the batteries were
> grid-exporting at same time of peak solar production. I can see the
> batteries charging at 23KW if charging from grid but of course solar can
> never be a load.  And exporting battery power simply not a financially
> smart option.
>
> So the only answer I can come up with is this transformer is serving more
> than this home and seems undersized by utility if it's serving multiple
> homes with 200-amp services. Few words from Oncor is that this is the issue.
>
> I alerted Oncor to the Power Control System capabilities to limit power
> export and they are insistent that 2KW is all they can take (they never
> said if this a import or export limit). I asked if this was a grid-tied
> system only with no ESS, would it have come back with the same 9KW (AC)
> limit? I think they are tripping over the combined connected capacity of
> solar + ESS.
>
> Anybody else in Texas running into this recently? I told Oncor I'd be
> perfectly fine with 9KW export capability (the solar) and limit
> grid-charging to this power, too.
>
> This isn't Hawaii...so I'm super surprised and about to lose a lot of
> money.
>
> *Howard "Scot" Arey*
> *Owner, Solar CenTex*
>
> NABCEP PV Installation Professional
> TECL 29755
> 254-300-1228
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251126/f25eeeb6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-cbrq1kwn.png
Type: image/png
Size: 294949 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251126/f25eeeb6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-cbrq1kwn.png
Type: image/png
Size: 294949 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251126/f25eeeb6/attachment-0001.png>


More information about the RE-Wrenches mailing list