Hey all –



I have to credit *Amos at Zonna Energy  *who provided the following
procedure for upgrading a Radian GS4048 to a Radian GS8048.



If you want to change a GS4048A to a GS8048A, add second power module & you
also need to change a setting in the inverter and change it to a GS8048A

Go to ;  *Lock>Up>Installer> Enter installer Password
1732>Settings>Inverter>Model Select** and spin wheel *to select the correct
model.



Thank you Amos!

_________________________________________________________

Dana Orzel                GREAT SOLAR WORKS!

C – 208.721.7003      E – dana at solarwork.com

W - www. greatsolarworks.com     www.solarwork.com

*“Responsible Technologies for Responsible People since 1988!”*

On Fri, Nov 21, 2025 at 10:28 AM Dana Orzel via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hey all –
>
>
>
> I have to credit *Amos at Zonna Energy  *who provided the following
> procedure for upgrading a Radian GS4048 to a Radian GS8048.
>
>
>
> If you want to change a GS4048A to a GS8048A, add second power module &
> you also need to change a setting in the inverter and change it to a GS8048A
>
> Go to ;  *Lock>Up>Installer> Enter installer Password
> 1732>Settings>Inverter>Model Select** and spin wheel *to select the
> correct model.
>
>
>
> Thank you Amos!
>
> _________________________________________________________
>
> Dana Orzel                GREAT SOLAR WORKS!
>
> C – 208.721.7003      E – dana at solarwork.com
>
> W - www. greatsolarworks.com     www.solarwork.com
>
> *“Responsible Technologies for Responsible People since 1988!”*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251123/cfe5a7a0/attachment.htm>


More information about the RE-Wrenches mailing list