[RE-wrenches] ATS for CRD Multimode Compliance

Zeke Yewdall zeke at darkforestsolar.com
Wed Nov 12 14:48:12 EST 2025


Travis.

Is this the UL1741 PCS CRD (usually cross listed with UL3141 listing) or is
this a different listing that they are looking for.  I was pretty sure that
the SolArk's all have the UL1741PCS CRD/UL3141, and of course the MID is
built into the inverter already.  But maybe it's a different one.

For California, they have an interesting issue for the open loop response
time for the PCS CRD listing -- you only need less than 10 second response
time for net billing systems, but less than 2 second response time for zero
export systems, which has been a harder target for a number of inverters to
hit (many are coming in at 3 to 4 seconds for one of the step tests).
Ironically one of the main reasons to do a zero export system is because
there is already a grandfathered net metered system on site which can
export, but they want the new system to have a very fast response time to
never export... I calculated that the inadvertent export could maybe cost
them a dollar or two a year worse case)

Zeke

As of July, New York State requires CRD Multimode compliance documentation
for any MID devices.
Sol-Ark does not yet have their paperwork.
Does anyone have a recommendation for an ATS that I can install upstream of
the Sol-Ark Inverters to satisfy this requirement?
It feels like all I "need" is a simple contactor that will open when the
grid goes down, but I don't know who makes a simple device like that which
is also UL Listed.

-Travis

-- 
Travis Knipple
Senior Engineer
Hudson Solar Solutions LLC
Rhinebeck, NY 12572
518-539-8040 x408 | travis at hudsonsolarsolutions.com

-- 
Zeke Yewdall
PV Engineer
NABCEP #031508-89
zeke at darkforestsolar.com
303-523-3592
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251112/4daeefe6/attachment.htm>


More information about the RE-Wrenches mailing list