Thanks Kevin, that is my distinct preference as well. But sometimes, if I
can get them halfway there, it seems like an improvement and makes the next
half step less painful for them.
On a separate note, I have both XW+ and XWpro inverters in the field, and
had not noticed the downgrade you mentioned, although I haven't made a
study of it either. I have an MIT retired Physics Department head as one of
my XWpro clients (dual stack) with 2 eVault Maxs. He has made a study of
the programming and all the odd glitches and undocumented impacts of
changing one part of the programming has on another seemingly unrelated
area of the programming. He has been pushing the limits of the programming
and often has to explain to Schneider level 2 tech support what he has done
to make the inverter behave in a way that maximizes his self consumption.
I guess my point is, he hasn't noticed the problems you referred to, so at
this point, I most certainly haven't.
Howie
Howie Michaelson
On Mon, Oct 27, 2025 at 12:38 PM Kevin Pegg via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> A word of caution – the XW Pro is, IMO a major downgrade from any previous
> XW’s. The newest firmware causes all sorts of power quality issues if you
> are running a generator. Like it literally smoked electronics for some
> clients. Schneider knows, they just don’t care. There’s good reason these
> units are going cheap now to dump obsolete inventory.
>
>
>
> XW Lithium integration is through the Insight Home or Gateway monitoring
> devices. It can be done, but in my experience it’s constantly glitching out
> and not delivering reliable power solutions to clients.
>
>
>
> I generally recommend to clients if they want newest battery tech, let’s
> upgrade the inverter as well. Less call backs.
>
>
>
> Kevin
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jay via RE-wrenches
> *Sent:* Monday, October 27, 2025 5:23 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jay <jay.peltz at gmail.com>
> *Subject:* Re: [RE-wrenches] Schneider XW+ and Midnite batteries
>
>
>
> I just had a conversation with someone about this the other day and he
> recommended buying an xw pro which he said has the latest firmware and can
> do lithium communication much easier than the older xw.
>
>
>
> I haven’t researched it but if true you can buy a new xw pro from NWS for
> under $900.
>
>
>
> Jay
>
>
>
> On Oct 26, 2025, at 9:42 PM, Howie Michaelson via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Has anyone successfully close-looped a Schneider XW+ with Midnite PF16
> batteries, or any other battery BMS that uses Pylon? I have a client that
> currently has an XW= running on a set of 2 volt Surrettes that are
> failing. I'd like to switch him out to an AIO/PF16 system, but want to
> give him the option of keeping the XW+ (which is paired with 2
> Outback150vDC Charge Controllers). The mixed brand Inverter-Charge
> Controller setup gives me some pause if keeping that, but if necessary, I
> just want to hear success stories if they are out there.
>
> Thanks,
>
> Howie Michaelson
>
> Sun Catcher
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251027/0a22b229/attachment.htm>
More information about the RE-Wrenches
mailing list