Hi Wrenches - Blast from the past here, I just saw a tech note from Tesla
that Eaton is recommending BR breakers with a H suffix for installations
with high continuous currents like solar inverters, battery inverters, and
EV chargers to avoid the risk of a thermal event.
https://www.eaton.com/us/en-us/skuPage.BR260H.html
According to the note in the catalog
https://www.eaton.com/content/dam/eaton/products/low-voltage-power-distribution-controls-systems/loadcenters-and-circuit-breakers-v1-t1-ca08100002e.pdf
[image: image.png]
-August
On Tue, Jan 21, 2020 at 9:39 AM August Goers <august at luminalt.com> wrote:
> Hi Jason -
>
> It certainly appears that there was some sort of surge or short. We've had
> a few cases where microinverter branch circuit end termination caps were
> left off or fell off and shorted out during rain storms. You might want to
> double check that those are all in place. We've also had cases were
> microinvers themselves developed internal shorts. This third comment is
> only anecdotal - I've been in touch with a couple of other installers that
> have had back-fed breaker issues specifically with Eaton brand breakers
> burning up the bus stabs. Our company has had one unexplained issue where
> the inverter output breaker bus stabs were burned up with Eaton breakers. I
> have no idea whether the breakers were faulty or what, but thought I'd just
> mention it in case there is a pattern.
>
> Best, August
> Luminalt
>
>
> On Tue, Jan 21, 2020 at 9:10 AM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> (System installed by another contractor...)
>>
>> I have been tasked with assisting in the investigation of damage in a
>> subpanel used to combine inverter output circuits (5 strings of
>> microinverters). There appears to be no damage to conductors or other
>> system components. It looks like the damage started at the stabs of the bus
>> bar where the breakers connect. Picture attached. Here are a few clues:
>>
>> - Monitoring indicates that damage occurred overnight a few weeks
>> ago. That night we had rain as a winter front came through Florida,
>> possibly lightning. The prior day everything was fine.
>> - The next morning, only 2 of 5 strings started producing power, but
>> 4 of 5 strings were reporting data to the Envoy. The two strings that were
>> reporting but not producing power reported 0Vac and Voc on the DC side of
>> the microinverters.
>> - A couple of weeks later, 1 of the 2 strings that was producing
>> power quit doing so, but continued reporting data.
>> - Customer discovered damage yesterday.
>> - About a week before the initial damage apparently manifested
>> itself, another contractor installed a whole house generator transfer
>> switch on the line side of the PV interconnection. The generator has never
>> been run (there is not even a LP fuel source on site yet). I pointed out
>> that the solar interconnection, which was previously on the supply side,
>> would need to be moved to the supply side of the generator transfer
>> switch's main breaker before operation. During the transfer switch
>> installation, the contractor also switched line 1 and line 2, but that
>> shouldn't really matter, except for Enphase consumption monitoring, which
>> was messed up by the swapping of the lines.
>>
>> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
>> place for lightning damage to manifest itself. I can't visually detect any
>> other damage anywhere else. I can't imagine that the transfer switch
>> installation would have anything to do with it, but the timing is
>> interesting. Other than replacing the subpanel and OCPD and firing it back
>> up (no pun intended), I'm not sure how to approach further investigation.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251024/7a42c33f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 64172 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251024/7a42c33f/attachment.png>
More information about the RE-Wrenches
mailing list