My interpretation, and the way it was explained to me by both Ryan Mayfield
and Kyle Bolger(several years ago at this point, popular opinion may have
changed since). Is that it is not a seperate service.
 It is however required to have a ground-neutral bond( though in my opinion
pointless and redundant as there is a bond in the enclosure where the tap
is made). If it gives you any issue, ensure as close to equal potential to
the grounding electrode as possible(and make sure your neutral is
appropriately sized). I personally don't see the point but it is an NEC
requirement




On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi All,
>
> For years I have understood that when doing a supply side connection, you
> are supposed to bond the neutral to ground in the solar service disconnect.
> I have a Midnite AIO system with two inverters (set up as a supply side
> connection) that recently was getting a CA-DC link Overvoltage error. When
> talking to Midnite, their first response was to make sure that there was
> only one N-G bond in the whole system. When I mentioned that the solar is a
> separate service and thus there is a N-G bond in both the main panel and
> the inverter distribution panel, they said to remove it from the inverter
> distribution panel. I want to make the system work right, but I also am
> hesitant to do something against how I have understood the NEC to be for a
> long time. I am curious if you all have thoughts on this or run into a
> similar situation.
>
> Cheers,
> Dave
>
> --
>
> [image: Logo] <https://www.sungineersolar.com/>
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd.
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>| Ithaca,
> NY 14850
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
> w: www.sungineersolar.com <http://www.sungineersolar.com/>
> c: (607) 270-0370
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251023/2bd9d6d9/attachment.htm>


More information about the RE-Wrenches mailing list