The supply side switch needs the Neutral-GEC bond. There should also be
one in the Main Service Panel. Although just looking at 250.142 (A) it
says "shall be permitted". So, that is a little confusing to me. I
always have had that bond for this type of connection. Chris
On 10/23/2025 9:07 AM, Dave Tedeyan via RE-wrenches wrote:
> Hi All,
>
> For years I have understood that when doing a supply side connection,
> you are supposed to bond the neutral to ground in the solar service
> disconnect. I have a Midnite AIO system with two inverters (set up as
> a supply side connection) that recently was getting a CA-DC link
> Overvoltage error. When talking to Midnite, their first response was
> to make sure that there was only one N-G bond in the whole system.
> When I mentioned that the solar is a separate service and thus there
> is a N-G bond in both the main panel and the inverter distribution
> panel, they said to remove it from the inverter distribution panel. I
> want to make the system work right, but I also am hesitant to do
> something against how I have understood the NEC to be for a long time.
> I am curious if you all have thoughts on this or run into a similar
> situation.
>
> Cheers,
> Dave
>
> --
>
> Logo <https://www.sungineersolar.com/>
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com <http://www.sungineersolar.com/>
> c: (607) 270-0370
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20251023/105cec1d/attachment.htm>
More information about the RE-Wrenches
mailing list