We have built DLO battery cables assemblies and have had a couple installations flagged by inspectors due to not having UL requirements (83 and 1581 if I remember correctly).
We mostly build battery assemblies with the two class K options - All-Flex or X-Flex

Here are a list of the UL certifications between the two:

DLO cable
(24AWG ASTM Class)
EPDM/CPE Insulation
-40°C - +90°C

    UL
44
1650
2556
2806


Cobra X-Flex and Direct Wire All-Flex
(30AWG ASTM -Class-K)
PVC insulation
-50°C – 75°C (Wet) / 105°C (Dry)

    UL
83
758
1063
1232
1283
1284
1337
1338
1339
1426
1581
1581
2556
2556
10070
10269





Bryan Norkunas

PV-Cables Inc.

989 Milton Ave Ste 1D

Ferndale CA 95536

(707) 923-3000 office

www.pv-cables.com<http://www.pv-cables.com/>

________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Tom McCalmont via RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Wednesday, September 3, 2025 5:02 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Tom McCalmont <tom.mccalmont at pairedpower.com>
Subject: Re: [RE-wrenches] Ferrules for large fine-stranded wire.

I’ve been monitoring this thread with interest and wanted to add some perspective since we have experience with this.

Listed lugs in combination with DLO cable are a good solution for connecting batteries to inverters.  The DLO cables are much more flexible at large wire sizes typical of battery cables, and listed lugs provide a safe method to connect the cables to the inverter that assures you will not lose strands in the connection.  Because DLO cable contains many strands and there is some amount of open space between those strands, the overall diameter of the DLO for a given gauge is higher than it will be for equivalent sized stranded THWN.  Therefore, you need to locate lugs that are appropriately sized specifically for DLO cable.

In addition, many of the crimping devices that I’ve seen pass through the group for attaching the lugs will not result in a listed connection, and they could create fire risk.  Screw lugs may not tighten appropriately on the fine strands of DLO as one commenter mentioned.  Hammer-type crimping tools may work to result in what feels like a firm connection, but there is no way to judge that you have hammered with the exact appropriate force to result in a listed connection.  The only sure-fire way to do so is with an over-center crimping tool that is listed for the purpose of attaching the specific lug you have selected to the cable type of a matching size.

These tools are very expensive, and I understand the pain of having to purchase the correct one.  We are all tempted by cheaper options.  But the pain of that one-time expense is likely to be much less than the pain of compensating a very unhappy customer following a fire started by a substandard connection.

As we all know, battery cables carry a lot of current, and substandard connections are much more likely to create fire risk than would be the case for high voltage, low current connections.  I hope this voice of experience is helpful!

Tom McCalmont, P.E.
CEO, Paired Power
pairedpower.com<http://pairedpower.com> | LinkedIn<https://www.linkedin.com/company/paired-power/>
Direct: (669) 877-2931

You're Invited:
Join us on Sept. 18th for a webinar conversation<https://us02web.zoom.us/webinar/register/WN_PEkYGlNuRfigHBWjtiec0A#/registration> on how Intuit has deployed Paired Power’s AI-driven solar microgrid system to add EV chargers at scale without new grid capacity, eliminating demand charges and revolutionizing the future of electric vehicle (EV) charging.

[https://pairedpower.com/wp-content/uploads/2025/08/webinar.png]

Register Now:
https://us02web.zoom.us/webinar/register/WN_PEkYGlNuRfigHBWjtiec0A#/registration

On Sep 3, 2025, at 4:33 PM, James Jarvis via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:

William,

None of the crimpers you sent photos of are for ferrules. Those are all lug crimpers. Some are barely that. Nobody should be seriously considering anything you hit with a hammer to be a proper tool for installing any type of connector.

Ferrule crimpers produce a square crimp and do what they are supposed to.

Last Wednesday I sent you a note with this link:
https://www.ferrulesdirect.com/collections/hand-crimping-tools/products/vag240

It makes a square shape and won't have weird edges and the artifacts you mention you get when you smoosh a ferrule with a non-ferrule crimper.

Ferrules are highly useful and reliable when installed correctly. You just need the right tool.

The other thing I mentioned last week were pin adapters. They are crimp on fittings that are rated for fine stranded wire and they convert it to course stranded or solid shape. Here was the example I sent:
https://www.ilsco.com/Ilsco/ccrz__ProductDetails?sku=F2C-1%2F0-1%2F0-ILSM-ILS&cclcl=en_US




Best regards,



-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/


On Wed, Sep 3, 2025 at 6:10 PM William Miller via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:

Friends:



My understanding is if the lug has a set-screw that contacts the strands, fine strands can wind around the set screw, get into the threads and not tighten adequately.  If you are crimping fine strands inside of some type of barrel your connection should be OK.



I had been using Outback until they imploded and all of the battery connections were via studs or bolts that required crimped-on rings.  Now I am back to set screw lugs and fine stranding became an issue again.



I did try another experiment: I took a 4/0 ferrule that would not fit into the Envy lugs and snipped a section out of it.  I curled it into a slightly smaller diameter and it fit into the lug.  I suppose one could cut the ferrule in half longitudinally and insert a portion of the ferrule between the set screw and the strands.



I am pleased with the copper sheeting wrapped around the fine strands.  That will be my SOP.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com<http://www.millersolar.com/>

CA Lic. 773985




From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Ray Walters via RE-wrenches
Sent: Wednesday, September 3, 2025 1:40 PM
To: re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>
Cc: Ray Walters
Subject: Re: [RE-wrenches] Ferrules for large fine-stranded wire.



I've got to ask: Are none of the lugs on these Chinese inverters approved for fine strand cable?  I just have not had a problem with that, but I've mostly used Magnum, Midnite, and Outback equipment over the years.   What were the lugs on the old Trace DC 250 boxes?  Were they fine strand rated?  They sure were tough to get 4/0 into, as William mentioned.

Ray
Remote Solar

On 9/3/2025 12:57 PM, Kent via RE-wrenches wrote:

William,

If the only reason the ferrule wouldn't fit after using the hex crimper was the ridge left where the dies meet, you could rotate the cable 120 degrees and crimp the ferrule again.

I doubt that the indenter crimper will do a decent job with large ferrules.

I do like your thin piece of copper solution. Not UL approved but I dare say wrench approved.

Kent Osterberg
Blue Mountain Solar



On 9/2/2025 8:55 PM, William Miller via RE-wrenches wrote:

Friends:



Thank you for all of your input on this question.  I feel it only right I report back how this turned out



I tried a crimper like this:





It left a jagged ridge on both sides of the ferrule where the dies met.



The crimper below was suggested but I have not tried it:



This was suggested but I have not tried it either:



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250904/1544db3a/attachment.htm>


More information about the RE-Wrenches mailing list