Thank you, It's pretty tight, I am hoping for some radio or wifi breaker
to send a signal. Just no luck yet. Chris
On 8/23/2025 9:37 AM, Drake Chamberlin via RE-wrenches wrote:
>
> P.S.
>
> You would need to run the control wires back to the inverter. Can you
> possibly run a pair of #16 wires the through the conduit feeding the
> building with the compressor?
>
> ---
>
>
> On 2025-08-23 09:30, Drake Chamberlin via RE-wrenches wrote:
>
>> Can you use a contactor with the coil wires connected to the AC IN of
>> the Outback? When incoming AC goes down, the contactor will open to
>> shed the compressor circuit.
>>
>> /Drake Chamberlin/
>>
>> /Athens Electric LLC/
>>
>> /Ohio Electrical Contractor’s License 44810/
>>
>> /NABCEP Certified PV Installation Professional/
>>
>>
>>
>> ---
>>
>>
>> On 2025-08-22 15:54, Christopher Warfel via RE-wrenches wrote:
>>
>> We installed a 4kW Outback multimode system about 8 years ago. An
>> electrician came in afterwards and installed 3 heat pumps on the
>> battery backed up power panels. The Outback inverter disconnected on
>> load every time there was a power outage. The electrician really
>> messed up and is long gone. Also found out did not pull a permit. But
>> I digress. We managed to move two of the heat pump circuit breakers
>> to the utility panel, so no longer on the battery backed up power
>> panels. The third heat pump is the problem as it is located in an
>> apartment building remote from the main house. The whole apartment
>> subpanel, including the heat pump load is interconnected to the
>> "main" battery backed up power panel in the home.
>>
>> A master electrician and I are considering how to shed the apartment
>> heat pump in a power outage. We cannot easily run a separate circuit
>> to the apartment building to pick up this load. We have considered a
>> smart panel, but the cost seems high for one circuit. Does anyone
>> know
>> of a power line product of RF product or similar that could operate
>> this breaker when the main service panel loses power? I have been
>> unsuccessful over months of sporadic research.
>>
>> Thanks in advance.
>>
>>
>> Chris
>>
>>
>>
>>
>>
>>
>>
>>
>> -- Christopher Warfel, PE ENTECH Engineering, Inc. PO Box 871, Block
>> Island, RI 02807 (401) 447-5773
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work,
>> try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250823/f25d5506/attachment.htm>
More information about the RE-Wrenches
mailing list