Can you use a contactor with the coil wires connected to the AC IN of
the Outback? When incoming AC goes down, the contactor will open to shed
the compressor circuit.
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio Electrical Contractor's License 44810_
_NABCEP Certified PV Installation Professional_
---
On 2025-08-22 15:54, Christopher Warfel via RE-wrenches wrote:
> We installed a 4kW Outback multimode system about 8 years ago. An
> electrician came in afterwards and installed 3 heat pumps on the
> battery backed up power panels. The Outback inverter disconnected on
> load every time there was a power outage. The electrician really
> messed up and is long gone. Also found out did not pull a permit. But
> I digress. We managed to move two of the heat pump circuit breakers
> to the utility panel, so no longer on the battery backed up power
> panels. The third heat pump is the problem as it is located in an
> apartment building remote from the main house. The whole apartment
> subpanel, including the heat pump load is interconnected to the
> "main" battery backed up power panel in the home.
>
> A master electrician and I are considering how to shed the apartment
> heat pump in a power outage. We cannot easily run a separate circuit
> to the apartment building to pick up this load. We have considered a
> smart panel, but the cost seems high for one circuit. Does anyone know
> of a power line product of RF product or similar that could operate
> this breaker when the main service panel loses power? I have been
> unsuccessful over months of sporadic research.
>
> Thanks in advance.
>
> Chris
>
> -- Christopher Warfel, PE ENTECH Engineering, Inc. PO Box 871, Block
> Island, RI 02807 (401) 447-5773
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250823/b2615f9b/attachment.htm>
More information about the RE-Wrenches
mailing list