We installed a 4kW Outback multimode system about 8 years ago. An
electrician came in afterwards and installed 3 heat pumps on the battery
backed up power panels. The Outback inverter disconnected on load every
time there was a power outage. The electrician really messed up and is
long gone. Also found out did not pull a permit. But I digress. We
managed to move two of the heat pump circuit breakers to the utility
panel, so no longer on the battery backed up power panels. The third
heat pump is the problem as it is located in an apartment building
remote from the main house. The whole apartment subpanel, including the
heat pump load is interconnected to the "main" battery backed up power
panel in the home.
A master electrician and I are considering how to shed the apartment
heat pump in a power outage. We cannot easily run a separate circuit to
the apartment building to pick up this load. We have considered a smart
panel, but the cost seems high for one circuit. Does anyone know of a
power line product of RF product or similar that could operate this
breaker when the main service panel loses power? I have been
unsuccessful over months of sporadic research.
Thanks in advance.
Chris