[RE-wrenches] Adding battery to grid tie

William Miller william at millersolar.com
Thu Aug 14 11:10:03 EDT 2025


I never said it was a good idea.

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Thu, Aug 14, 2025 at 7:48 AM Zeke Yewdall via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> While the AC coupled PV system can be added to the AC backed up loads
> panel, this defeats a lot of the functionality of a dedicated AC coupled PV
> array input on the AIOs and is not recommended by most of them.   In
> theory, yes, it works on most inverters to just add it as a negative AC
> load -- and I've even AC coupled an old Trace SW, and it works fine on
> that, despite being designed and built before AC coupling was thought of.
>
> But, if it's just on the AC loads output, the inverter does not have the
> ability to drop the AC PV array separately from the load if it needs to for
> high battery charge regulating, does not have the ability to measure the PV
> array input on monitoring, and may have other issues.
>
> Zeke
>
> > *Subject:* Re: [RE-wrenches] Adding battery to grid tie
> >
> > Correct me if I'm wrong:  I believe AIOs can accept AC coupled power
> > through the load 'output' port. That leaves the Grid and Gen inputs free
> > for their roles as labelled.
> >
> > The AC coupled inverters connect via a breaker in the critical loads
> > panel.
> >
> >
> > William Miller
> > Miller Solar.com
> > 805-438-5600
> > www.millersolar.com
> >
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250814/b544e99a/attachment.htm>


More information about the RE-Wrenches mailing list