[RE-wrenches] Adding battery to grid tie

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Tue Aug 12 10:05:55 EDT 2025



17.1 Connection to the Off-Grid Power System
(Protected Loads Panel)

SI5048U-TUS121440 | TBEN-SI5048U | Version 4.0

I've seen it elsewhere in SI literature also. It seems like a good 
descriptive designation that won't interfere with NEC definitions.

_Drake Chamberlin_

_Athens Electric LLC_

_Ohio Electrical Contractor's License 44810_

_NABCEP Certified PV Installation Professional_

---

On 2025-08-11 17:17, Chris Schaefer via RE-wrenches wrote:

> Dave,
> 
> Well that's a new term I've never heard before. Please explain the 
> Florida Hurricane Tap sir. Is this perhaps for generator use?
> 
> Christopher
> 
> On Mon, Aug 11, 2025 at 9:41 AM Drake Chamberlin via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> I use the Sunny Island designation of "Protected Loads."
> 
> ---
> 
> On 2025-08-09 13:54, jay via RE-wrenches wrote:
> 
> Yeah I've given up trying to correct people on that one.
> 
> On Aug 9, 2025, at 11:26 AM, Foxfire Energy via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Umm, just an FYI, I actually got dinged for labeling the AC output 
> panel from a battery backup inverter as "Critical Loads".. Critical 
> loads (Critical Branch circuits) are defined in article 100 of the NEC 
> as circuits associated with Patient Care.. AC loads from battery backup 
> inverters are more appropriately defined as "Dedicated Loads"..
> Maybe someone could correct me here, but I'm under the impression most 
> garden-variety inverters are not rated for Critical Load applications.
> db
> 
> -------------------------
> 
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf 
> of William Miller via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Sent: Saturday, August 9, 2025 1:03 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Cc: William Miller <william at millersolar.com>
> Subject: Re: [RE-wrenches] Adding battery to grid tie
> 
> Correct me if I'm wrong:  I believe AIOs can accept AC coupled power 
> through the load 'output' port. That leaves the Grid and Gen inputs 
> free for their roles as labelled.
> 
> The AC coupled inverters connect via a breaker in the critical loads 
> panel.
> 
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com [1]
> 
> On Sat, Aug 9, 2025 at 9:50 AM david quattro via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> True.  if you want to do grid, gen, and AC Couple then you need a 
> transfer switch or contactor.
> Likewise I haven't touched a Powerwall, nor an Enphase battery.
> 
> On Sat, Aug 9, 2025 at 9:36 AM jay via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> One big issue with the AIO's is that you can't do grid, generator and 
> ac coupling to the best of my understanding
> 
> I do like the idea of just removing the old GT inverter and stuffing 
> that into the AIO, elegant
> 
> yes its my understanding that Tesla won't accept generator.  While many 
> are pissed off at eg4, I won't touch tesla.
> 
> and FYI you can buy the same inverter at Fortress.
> 
> thanks everyone.
> 
> jay
> 
> On Aug 9, 2025, at 10:28 AM, Tyrone Houck via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Midnite AIO and Sol-Ark both work great for AC coupling in my 
> experience. If anyone is new to "All In One" inverters I recommend 
> having tech support walk you through commissioning, check firmware, 
> etc. the first time.
> 
> On Sat, Aug 9, 2025, 8:47 AM William Miller via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote: Two options:
> 
> 1. AC couple existing inverter to a battery capable inverter.
> 
> 2. Replace existing inverter.
> 
> I favor option 2.
> 
> Option 1 is only preferred if gaining access to the existing inverter 
> for replacement is difficult. An example would be a micro-inverter 
> system.
> 
> New AIO inverters allow true high voltage PV input so the existing 
> stringing will probably not need to be modified.
> 
> I'm new to this so type of upgrade so I welcome any corrections to 
> these opinions.  I did replace a Sunny Boy in my shop with a Soul Ark 
> and it's working great!
> 
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com [1]
> 
> On Sat, Aug 9, 2025 at 8:26 AM Jay via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote: Is there a consensus as to 
> what equipment to use for adding battery backup to normal GT inverter?
> 
> I've had a few people ask and I actually haven't done it.
> 
> Thx
> Jay
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org [2]
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [3]
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org [2]
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [3]
  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org [2]

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org [3]

  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org [2]

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org [3]

  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org [2]

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org [3]

  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

   --

Chris Schaefer's

Tel 585-229-2083 or Cell 585-748-1870
5115 S Hill Road ~ Canandaigua New York 14424
_www.solarandwindfx.com [4] ~ E-mail: chris at solarandwindfx.com_

Thomas Jefferson, the author of our great Constitution, once said, 
"democracy" will cease to exist when you take away from those who are 
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://www.millersolar.com/
[2] http://re-wrenches.org/
[3] http://www.members.re-wrenches.org/
[4] http://www.solarandwindfx.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250812/2c2f65b4/attachment.htm>


More information about the RE-Wrenches mailing list