[RE-wrenches] Battery RSD

Sue Stankevitz Sue at midnitesolar.com
Wed Jul 30 07:26:58 EDT 2025


The Birdhouse was designed to meet NEC 2014 string level rapid shutdown standards. As the industry moved on to modular level requirements demand for it dropped and it was discontinued.

Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:image001.gif at 01DC0123.54857DB0]

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Blair May via RE-wrenches
Sent: Tuesday, July 29, 2025 5:47 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Blair May <tump3391 at gmail.com>
Subject: Re: [RE-wrenches] Battery RSD

Sue what happened to the Birdhouse. My e panel has shunt tripped 250A battery breakers that is acquitted outside the building.
Tump

Blair "Tump" May

On Tue, Jul 29, 2025, 1:09 PM Sue Stankevitz via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
Midnite does not offer an outdoor rated enclosure for our large breakers but if only 100a was needed as Mike was asking about our MNPV3 with an MNEPV100(100a DC breaker) would be outdoor rated and lockable.

Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:image001.gif at 01DC0123.54857DB0]

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of MD Electric & Solar via RE-wrenches
Sent: Tuesday, July 29, 2025 12:46 PM
To: jay <jay.peltz at gmail.com<mailto:jay.peltz at gmail.com>>
Cc: MD Electric & Solar <mdelectricsolar at gmail.com<mailto:mdelectricsolar at gmail.com>>; RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Battery RSD

Wondering if Midnight solar makes something outdoor rated, with a typical 250ADC breaker, like this:
Outdoor rated, lockable....
https://www.midnitesolar.com/productPhoto.php?product_ID=76&productCat_ID=8&sortOrder=5&act=p

On Tue, Jul 29, 2025 at 9:39 AM jay <jay.peltz at gmail.com<mailto:jay.peltz at gmail.com>> wrote:
Maybe if you left the key on a chain to open the door, and placard with instructions on the outside that would work?


On Jul 29, 2025, at 10:23 AM, MD Electric & Solar <mdelectricsolar at gmail.com<mailto:mdelectricsolar at gmail.com>> wrote:

Correct, it does not have an external disconnect, but if you open the cover, each battery has it's own disconnect and the Sol-Ark has a battery disconnect.
Looks like I'm in the market for a 100 amp rated outdoor, lockable DC rated knife switch.
Mike

On Tue, Jul 29, 2025 at 9:16 AM jay <jay.peltz at gmail.com<mailto:jay.peltz at gmail.com>> wrote:
I had to look up that battery enclosure and if I understand correctly it does not have an external breaker/disconnect so yes the inspector is correct in the need for one if I understand.

jay





On Jul 29, 2025, at 10:09 AM, MD Electric & Solar <mdelectricsolar at gmail.com<mailto:mdelectricsolar at gmail.com>> wrote:

Here is the reference, attached.

On Tue, Jul 29, 2025 at 8:49 AM jay <jay.peltz at gmail.com<mailto:jay.peltz at gmail.com>> wrote:
I’ll let the code experts chime in, but I would ask for the code reference they are referring to.

The only one I can think of has to do with if the batteries are on the other side of a wall.

 Thats as clean an install as they come

jay



> On Jul 29, 2025, at 9:43 AM, MDElectricSolar <mdelectricsolar at gmail.com<mailto:mdelectricsolar at gmail.com>> wrote:
>
> <image0.jpeg>
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.com<http://www.mdelectricsolar.com/>
> www.facebook.com/mdelectricandsolar<http://www.facebook.com/mdelectricandsolar>
>
>
>> On Jul 29, 2025, at 8:06 AM, Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>
>> What is the layout of the equipment
>>
>> Are the batteries next to and therefore in sight of the inverter?
>>
>> Jay
>>
>>> On Jul 29, 2025, at 8:44 AM, MDElectricSolar via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>
>>> Wrenches,
>>> I have a building inspector in my county of Sonoma who has just told me that we need to install a rapid shutdown switch of some type between my LFZ battery bank and my Solark 15k inverter. He mentioned some type of knife switch within 5 feet of the equipment. I cannot find any reference to this requirement anywhere but he insists it is required. These batteries happen to be simplify or brakes and Stratton batteries and each battery has its own 80 amp breaker on the battery and the Solark has a battery disconnect switch built-in. We do have module level RSD which kills the solar output as well as the inverter output when the button is pushed. Does anyone have any experience with this or can they point me to the correct code section or what are others doing to comply with this requirement?
>>>
>>>
>>> Michael D Nelson
>>> MD Electric & Solar, Inc.
>>> 707-684-0064 mobile
>>> 707-884-1862 office
>>> www.mdelectricsolar.com<http://www.mdelectricsolar.com/>
>>> www.facebook.com/mdelectricandsolar<http://www.facebook.com/mdelectricandsolar>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
>>


--
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-412-3181
Cell: 707-684-0064
www.mdelectricsolar.com<http://www.mdelectricsolar.com/>
www.facebook.com/mdelectricandsolar<http://www.facebook.com/mdelectricandsolar>


<PRMD BLD_20250728_062230.pdf>



--
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-412-3181
Cell: 707-684-0064
www.mdelectricsolar.com<http://www.mdelectricsolar.com/>
www.facebook.com/mdelectricandsolar<http://www.facebook.com/mdelectricandsolar>





--
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-412-3181
Cell: 707-684-0064
www.mdelectricsolar.com<http://www.mdelectricsolar.com/>
www.facebook.com/mdelectricandsolar<http://www.facebook.com/mdelectricandsolar>


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250730/70c21bbc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 4417 bytes
Desc: image001.gif
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250730/70c21bbc/attachment.gif>


More information about the RE-Wrenches mailing list