[RE-wrenches] Battery RSD

jay jay.peltz at gmail.com
Tue Jul 29 12:16:10 EDT 2025


I had to look up that battery enclosure and if I understand correctly it does not have an external breaker/disconnect so yes the inspector is correct in the need for one if I understand.

jay





> On Jul 29, 2025, at 10:09 AM, MD Electric & Solar <mdelectricsolar at gmail.com> wrote:
> 
> Here is the reference, attached.
> 
> On Tue, Jul 29, 2025 at 8:49 AM jay <jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>> wrote:
>> I’ll let the code experts chime in, but I would ask for the code reference they are referring to.
>> 
>> The only one I can think of has to do with if the batteries are on the other side of a wall.
>> 
>>  Thats as clean an install as they come
>> 
>> jay
>> 
>> 
>> 
>> > On Jul 29, 2025, at 9:43 AM, MDElectricSolar <mdelectricsolar at gmail.com <mailto:mdelectricsolar at gmail.com>> wrote:
>> > 
>> > <image0.jpeg>
>> > Michael D Nelson
>> > MD Electric & Solar, Inc.
>> > 707-684-0064 mobile
>> > 707-884-1862 office
>> > www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
>> > www.facebook.com/mdelectricandsolar <http://www.facebook.com/mdelectricandsolar>
>> > 
>> > 
>> >> On Jul 29, 2025, at 8:06 AM, Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>> >> 
>> >> What is the layout of the equipment
>> >> 
>> >> Are the batteries next to and therefore in sight of the inverter?
>> >> 
>> >> Jay
>> >> 
>> >>> On Jul 29, 2025, at 8:44 AM, MDElectricSolar via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>> >>> 
>> >>> Wrenches,
>> >>> I have a building inspector in my county of Sonoma who has just told me that we need to install a rapid shutdown switch of some type between my LFZ battery bank and my Solark 15k inverter. He mentioned some type of knife switch within 5 feet of the equipment. I cannot find any reference to this requirement anywhere but he insists it is required. These batteries happen to be simplify or brakes and Stratton batteries and each battery has its own 80 amp breaker on the battery and the Solark has a battery disconnect switch built-in. We do have module level RSD which kills the solar output as well as the inverter output when the button is pushed. Does anyone have any experience with this or can they point me to the correct code section or what are others doing to comply with this requirement?
>> >>> 
>> >>> 
>> >>> Michael D Nelson
>> >>> MD Electric & Solar, Inc.
>> >>> 707-684-0064 mobile
>> >>> 707-884-1862 office
>> >>> www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
>> >>> www.facebook.com/mdelectricandsolar <http://www.facebook.com/mdelectricandsolar>
>> >>> 
>> >>> _______________________________________________
>> >>> List sponsored by Redwood Alliance
>> >>> 
>> >>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>> >>> 
>> >>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>> >>> 
>> >>> Change listserver email address & settings:
>> >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>> 
>> >>> There are two list archives for searching. When one doesn't work, try the other:
>> >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >>> 
>> >>> List rules & etiquette:
>> >>> http://www.re-wrenches.org/etiquette.htm
>> >>> 
>> >>> Check out or update participant bios:
>> >>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> >>> 
>> >> _______________________________________________
>> >> List sponsored by Redwood Alliance
>> >> 
>> >> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>> >> 
>> >> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>> >> 
>> >> Change listserver email address & settings:
>> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >> 
>> >> There are two list archives for searching. When one doesn't work, try the other:
>> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >> 
>> >> List rules & etiquette:
>> >> http://www.re-wrenches.org/etiquette.htm
>> >> 
>> >> Check out or update participant bios:
>> >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> >> 
>> 
> 
> 
> 
> --
> Michael D Nelson
> MD Electric & Solar Inc.
> Office: 707-412-3181
> Cell: 707-684-0064
> www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
> www.facebook.com/mdelectricandsolar <http://www.facebook.com/mdelectricandsolar>
> 
> 
> <PRMD BLD_20250728_062230.pdf>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250729/7d5768ad/attachment.htm>


More information about the RE-Wrenches mailing list