[RE-wrenches] Midnite AIO Battery Low/Lost Behavior

William Miller william at millersolar.com
Tue Jul 15 18:41:18 EDT 2025


Friends:

Could one set the inverter LBCO slightly above the battery LBCO?  The
inverter is controlling the shut down and the battery does not go into
alarm.


William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Tue, Jul 15, 2025 at 2:26 PM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> I can’t agree more that auto restart is a requirement.
> A well designed system that has the inverter shut off( shut down or not
> sure what the correct term is) due to low battery should restart in the
> morning.
>
> Now I could easily see that it will have to get to some X amount of SOC or
> volts or watts of input before it connects the AC loads.
>
> Jay
>
>
>
> On Jul 15, 2025, at 3:21 PM, Chris Schaefer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> 
> Mr. Bryce,
>
> As offgrid is our biggest piece of the pie, I too would like to have the
> AIO power back up when voltage is at an acceptable level just as our OB's,
> Magnum's and Xantrex's have been for years. My hope is that in the very
> near future a firmware upgrade would make this a selectable feature.
>
> Much appreciated,
> Christopher
>
> On Tue, Jul 15, 2025 at 4:35 PM William Bryce via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Is this closed loop or open loop?  If closed loop the "rules" require the
>> machine to stay shutdown until the "issue" is identified.
>>
>> On Tue, Jul 15, 2025 at 8:04 AM Tyrone Houck via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> That's my understanding as well. Sure would be cool if there was an
>>> automatic reconnect mode that could be set.
>>>
>>>
>>>
>>>
>>> On Tue, Jul 15, 2025, 7:56 AM Jason Szumlanski via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> With this new breed of AIO inverters, when the battery reaches low
>>>> voltage disconnect, do they all need manual intervention to restart
>>>> inverting?
>>>>
>>>> I'm having an issue with a Midnite AIO with a stack of Pytes batteries
>>>> that reset themselves for a yet undiagnosed reason. The DC Battery voltage
>>>> goes to zero on the inverter for a moment, and then returns. The problem
>>>> is, it requires manual intervention to push the button to turn the inverter
>>>> back on. It does not happen automatically. That's not good for an unmanned
>>>> remote site.
>>>>
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
> Chris Schaefer’s
>
>
> *Tel 585-229-2083 or Cell 585-748-1870 *
> *5115 S Hill Road ~ Canandaigua New York 14424
> <https://www.google.com/maps/search/5115%0D%0AS+Hill+Road+~+Canandaigua+New+York+14424?entry=gmail&source=g>**www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250715/06561669/attachment.htm>


More information about the RE-Wrenches mailing list